hi,

just needed a bit of advice.

ive bought a 10.5kw shower installed it with 10mm cable and a 45a pull cord. I cant seem to find a 45a legrand mcb anyway will it be okay to use a 50a legrand one?

thanks paul
 
if your 10mm is ref. method C,E or B, you'll just get away with a 50A MCB. if in an insulated wall, the CCC is only 43A.
 
yes. the 45A is the max. continuous load that the pull switch will handle. it's not a trip value.
 
i dont think their common for most brands now Paul.....its the same as 25A MCBs..their listed in BS7671.....but you try lookin for em in...lets say screwfix...or summat like that....
the thing is though Paul....if you don`t know/cant verify the installation method used...then as Tel has pointed out.....
so go under for you OPD rather than over...protect your install....
and don`t forget that manufacturers often overrate their products....
once you`v juiced it up...stick it on full whack....clamp it.....you may get a surprise
 
dont forget Paul....your protecting your cables......you cant verefy the installation method for em....so you have to work on worst case (within reason)....your the designer....so you make the call...
 
2 thoughts:

1. If its a pull cord switch ALWAYS use the Crabtree 50A
2. Fit a 40A breaker
 

Reply to shower mcb question in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock