Discuss Shower Pullcord in the Australia area at ElectriciansForums.net

S

Sparky Stu

I am an adult trainee and i am trying to understand a problem that i must have with my shower pullcord isolater in my bathroom. Recently it has burnt out and was wondering what has caused this, as i have replaced this isolator a few times over the years.

The neutral cable on the load side is the cable that has always burnt out. The cable is 10mm and the length of run cannot be that great as c/u is located in the kitchen directly under my bathroom. The shower is 8.5kw on a 40A 60898 MCB.

Each time i have replaced this pullcord i have stripped the cable back to where the cable is in good condition. Just looking for some possible answers as cable is now beginning to get a bit on the short side from all the previous stripping back. Cheers Stu :)
 
It sounds like the neutral is loose!

It could be that the 10mm cable is a bit too big for the terminals and not in properly. The design current is only 37a therefore you can get away with 6mm cable!

Also what is the rating of the switch?

Mark
 
as above, buy an mk one or similar, cheaper ones are likely to burn out, especially if kids use the shower as they are in there ages. tighten those screws up real tight
 
Also make sure you use the units, power on/off switch to actually turn the shower off. Quite often people just use the pull cord to turn the shower off and therfore your switching under load, which will reduce the life of perhaps cheaper switches.
 
I only fit the 50amp Crabtree ceiling pull switch now as the old 45amp square ones are difficult to wire and prone to suffer from loose connections and burning out. The Crabtree is well designed and easy to wire with 10mm cable, also when you remove the cover the neon is removed as well. IMHO a very well thought out piece of kit and well worth checking out.
 
It is most likely to be a poor connection at the screw-in terminal on the switch. I've seen this lots of times in all sorts of fittings.

Make sure the screw is really tight, the inside of the terminal is clean, and the wire is also clean. Check the other screws as well.
Alan.
 
Thanks for all your replys, normally i make sure that the terminals are tight. Just had a thought that if the cable was stripped so that the amount of cable showing to be terminated was too long could this pertrude from the other end of the terminal and cause arking therefore resulting in the switch burning out?
 
Pretty much always going to be poor connections that cause burning at cable terminations. As others have said it could also be poor quality switch gear.
 
Crabtree 50A pull switch each and every time!!! As your wiring slack is almost gone now, buy the best and reject the rest, next time it's a rewire job!! lol!!!
 
When terminating stranded cable over 6mm i tighten the terminal, wiggle the wire back and forward slightly and tighten again. This seems to settle the strands and the screw almost always goes another quarter turn. Never had wire overheat yet. ( i shoulnt have said that should i)
 
A friend on mine asked me to connect up a electric shower today 10.5kw and a 45 amp pull cord isolator located in zone 1 about 300mm from shower head.It was inside the shower screen side of the bath !!!
I said no and he got the hump because the client asked him to put it there and he does not have enough cable to relocate it.It also finished tiled but yet to be grouted.
She was not keen on having it outside the bathroom and she also did not want to have a extractor fan fitted because of the noise !
Wish I was never asked.
I said isolator should be 3 metres away or outside room.
Back tomorrow for a chat and a biscuit and probably leave him some 10 twin & earth.
 
As most of the other guys have said - loose neutral. Recently had a similar incident on a main incomer chattering on the neutral - wasn't picked up on routine maintenance. Ended up costing a load of moolah!
 
A friend on mine asked me to connect up a electric shower today 10.5kw and a 45 amp pull cord isolator located in zone 1 about 300mm from shower head.It was inside the shower screen side of the bath !!!
I said no and he got the hump because the client asked him to put it there and he does not have enough cable to relocate it.It also finished tiled but yet to be grouted.
She was not keen on having it outside the bathroom and she also did not want to have a extractor fan fitted because of the noise !
Wish I was never asked.
I said isolator should be 3 metres away or outside room.
Back tomorrow for a chat and a biscuit and probably leave him some 10 twin & earth.

A pull cord isolator does not have to be 3m away. A DP switch does. A pull cord can be located 600mm away from the edge of shower basin. It can also be located in zone 1 if the switching mechanism on the ceiling is 2.25m from the basin floor.
 
Many thanks SimpleSimon.
Your spot on as per OSG but I am amazed that you could have a pull cord switch within zone 1 at all.I would never have it in my house with all that condensation in the shower,seems daft.
I must confess that all shower fitted I always locate a DP isolator outside,don't like pull switches seems old fashioned to me.
Thanks again.
 
Also make sure you use the units, power on/off switch to actually turn the shower off. Quite often people just use the pull cord to turn the shower off and therfore your switching under load, which will reduce the life of perhaps cheaper switches.

Thank you Malcolm, I don't really do domestic, but even I know that you MUST advise customers to NOT use the pull cord as an on/off switch. Hence the reason that I was taught to always shorten the cord, so that an adult would have to stretch to reach it.
 
Many thanks SimpleSimon.
Your spot on as per OSG but I am amazed that you could have a pull cord switch within zone 1 at all.I would never have it in my house with all that condensation in the shower,seems daft.
I must confess that all shower fitted I always locate a DP isolator outside,don't like pull switches seems old fashioned to me.
Thanks again.

I use pull cords but would never put in Zone 1 either for same reasons. Plus the string gets too wet n rotten.
 

Reply to Shower Pullcord in the Australia area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
382
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
709
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock