Hello. Can anybody please help. I've been in my house for 5 years and had no trouble with shower at all. A couple of weeks ago the wife says that shower wasn't working. I looked at circuit board and mcb had tripped. Flicked switch back on and everything was ok. Went for a shower later and its tripped again. Flicked it back on and it worked again. Thought shower might be knackered with being old so put a new shower in. 8.5kw with 32a mcb. Same problem.
I can flick mcb on and it will stay on, I can have a shower and it stays on, when I turn shower off it still works but a few minutes after I turn shower off it trips mcb. Any ideas off what the problem is will be greatly appreciated. Thanks
 
Is it the same 32 amp MCB that you have always had? If it is then it could be getting tired.A 8.5kw shower can pull approx 38 amps which is stressing the 32amp mcb.Over time they get lazy and trip even more.I would recommend changing the mcb to a 40 amp and see how it goes.Don't forget that since Jan 1 ,the replacement mcb has to be the same make and model as the original.You can usually source one off Ebay if your local wholesalers doesn't have one.
 
Hi V and Welcome to the Forum!
I suspect you're going to need some help to fix this as it could be a wiring fault (is it mcb or rcbo?) or a tired mcb as per Bob.
 
Whilst the advice on the mcb made be reasonable, who is to say the cable is big enough?

Unless you have competence and test kit, rushing to upgrade a mcb could have unpleasant consequences ....
 
It's a fixed load, changing the mcb for a higher rating will have no effect on overload protection, which is not required, only fault protection will be affected.
agreed, but OP needs to determine if the cable is the correct size for the load, ref. method being taken into account.
 
Thanks for the advice. I believe the current mcb is a Lewden one. Does that mean I have to get it swapped with another lewden. Why can i not use something like a Wylex if it's the same ampage
 
Thanks for the advice. I believe the current mcb is a Lewden one. Does that mean I have to get it swapped with another lewden. Why can i not use something like a Wylex if it's the same ampage

Have you read post #7?

And no you can't fit any manufacturer .... some won't fit at all and we are now on the 18th edition which specially stops it
 
Thanks for the advice. I believe the current mcb is a Lewden one. Does that mean I have to get it swapped with another lewden. Why can i not use something like a Wylex if it's the same ampage
As above, it is now a departure from the regulations to fit a device from a different manufacturer, unless you want to be legally responsible for the design of your DB if a fire was caused.
 
It's a fixed load, changing the mcb for a higher rating will have no effect on overload protection, which is not required, only fault protection will be affected.
On about upping the cable size to suit the protective device, though.
 
Hi - my best advice is to get someone in to help you fault find. You should not be opening up your consumer unit and changing circuit breakers, just saying.
 
It's a fixed load, the load will be 8.5kw regardless of the rating of the protective device. Overload protection is not required, only fault protection.
Matters not. I am not saying up the breaker.....but if you do up it, the cable should also be upped accordingly for cable protection. That protection is needed, even though you are not varying the load. Just regulation, that's all.
 
I wouldnt fancy showering under a electric shower that's tripping the mcb.

Get the circuit tested, rcbo fitted and replace the shower if necessary.
 

Reply to Shower tripping mcb after being used in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
985
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
Replies
10
Views
2K
I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine...
Replies
8
Views
822
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
762

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock