How can I calculate ? How do I know what size cable I need?

9.5 kW shower
40 C ambient temperature
T+E cable installed in loft space
25m length of run
type B breaker

In 9500\230 = 41.30A
In 42A
 
Hi MMJ,
Have a look in your BS7671 book and that will give the cable calcs & derating factors for installation method needed.
 
9500/240 = 39.6A. use a real voltage, not some half baked euro nonsense.
 
25m is a good old run

As the OP has stated "T+E cable installed in loft space"

I wonder how much of that run is in the insulation in the loft?
 
if it's run properly, none. till the free insulation monkeys come in.
 
If running any cables through an empty un-insulated loft you need to assume insulation will be installed in the future, its one of those cable designs you need to account for other trades in design :)
 
run the cable up and over where any insulation may be thrown in.
 
"Any warming up,of the cable,running through loft insulation,will be counter-acted by the cooling effect of running up,the cavity..."

^^ I heard this off a time-served lad,who does all the install,for a large kitchen/bathroom retailer...:20:
 
"Any warming up,of the cable,running through loft insulation,will be counter-acted by the cooling effect of running up,the cavity..."

^^ I heard this off a time-served lad,who does all the install,for a large kitchen/bathroom retailer...:20:
And how does he take into account that somewhere down the line someone may blow glued polystyrene insulation into the cavity containing said cables ?
 
How can I calculate ? How do I know what size cable I need?

9.5 kW shower
40 C ambient temperature
T+E cable installed in loft space
25m length of run
type B breaker

In 9500\230 = 41.30A
In 42A

Two problems with your calculation, the 9500w rating will be at 240V not 230V and you have calculated Ib not In. In should be selected based on Ib
 
Shower

Hi is anyone tell what cable can I use for 9.5 kW shower . Plz I think it's 10mm and 40A but I m not sure.



(Threads merged from this point)
 
Last edited by a moderator:
Re: Shower

Depends on many things: length of run : installation method etc etc. are you an electrician?
 
Re: Shower

to be honest, if you don;t know how to calculate cable and OCPD sizes, i don't think you should be considering doing this. if you are in training, and this is hypothetical, then say so, and assistance will be forthcoming.
 
Re: Shower

morning pete. wet the bed?
 

Reply to Shower wire in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock