Job is to replace this extractor fan as in attached photograph, would you say its in zone 1 or 2, i.e. could I replace with mains or would selv be needed not sure if I can get above ceiling to fit transformer.Shower zone.JPG
 
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
Advertisement - Content continues below

telectrix

-
Mentor
Arms
Esteemed
230V fan is OK in zone 1 as long as it's IP44. or bettewr.
 
And manufacturers instructions followed...
I had similar situation and Vent Axia tech said no. Answer: fitted the Manrose!
 

Dave OCD

-
Mentor
Arms
Esteemed
In the case of this particular unit with the positioning and height in relation to the shower I'd be looking at a 12 volt fan, although if that's a flat roof or very low pitch fitting the transformer unit could be a bit challenging.
 

telectrix

-
Mentor
Arms
Esteemed
fit a IP44 230V fan end of.
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Shower Zone and fan in the Electrical Forum area at ElectriciansForums.net

Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom