Job is to replace this extractor fan as in attached photograph, would you say its in zone 1 or 2, i.e. could I replace with mains or would selv be needed not sure if I can get above ceiling to fit transformer.Shower zone.JPG
 
230V fan is OK in zone 1 as long as it's IP44. or bettewr.
 
In the case of this particular unit with the positioning and height in relation to the shower I'd be looking at a 12 volt fan, although if that's a flat roof or very low pitch fitting the transformer unit could be a bit challenging.
 

Reply to Shower Zone and fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Buying a replacement extractor fan. It falls into zone one with the room setup. Looking at two fans. One is rated zone 1 one is rated zone 2...
Replies
2
Views
524
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
665
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
296

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock