I have a 3amp fused spur. Off this I have a transformer to step down to 12v dc 3A.

I've got 2 devices plugged into this transformer, one has 2.5amp on the label, the other has 1amp on the label. Would I be right in assuming these are standard running amounts and so will immediately blow the fuse? If so, what would be the approach to accommodating these devices? Increase the 3amp to something bigger and add a new transformer?

Thanks in advance
 
A 3A power supply will run hot and fail early if you are drawing 3.5A from it for an extended length of time.

Remember that 3A is the output of the power supply at 12v
The fused spur is feeding the Input of the power supply at 230v
This roughly equates to a current of 0.2A from the fused spur.

So the fuse will not fail.
 

Reply to Simple amp question (label on UK devices) in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock