Discuss Single phase supply in the Electrical Forum area at ElectriciansForums.net
Justin that is a dual voltage motor but I cant understand the configuration of the brass factory jumpers which could possibly go phase to phase as stated above the name plate should have all the info you need to know. It should read 3 phase or single phase motor. I’ve never seen a 480vac motor that wasn’t 3phase and the flex is no factor at allThere would be three wires in either case. If it is 240V, they will be active, neutral and earth. On a standard split-phase 480V system there would be two actives and earth, with no connection to the neutral. You can usually identify which voltage the motor is set up for, by comparing the positions of wires and links in the terminal box with the diagram that is usually inside the lid. If in any doubt, post pics of the above plus the data plate.
here are some photos
View attachment 58668View attachment 58669View attachment 58672
I read your profile and being a trainee your boss should have to tell you what it was before hand. My friend if you are not 100% positive of the voltage and 3 phase or single or single phase. I’m worried about you wiring that motor not knowing more than you know. Call the manufacturer where you bought that motor for more information. If your boss is so sure about the voltage and wiring let him wire it up. Under no circumstances should you wire that motor. With the factory jumpers is for wiring it in a star or delta configuration Good luckMy only concern is I isolated and disconnected in a hurry and had to order a new motor and order a single phase 240v motor assuming the supply was 240v, now my boss is saying it’s configured for 480v supply and asking if I’m sure the supply was 240v.
We would like to advise you but we have no way of knowing the voltage or single or 3 phase and I cannot steer you in the right direction. Tell you boss I said that it is to dangerous for you to wire. Let this be a lesson and don’t get in a hurry to disconnect it and take pictures and draw how it’s wired before you unhook it. If we had pictures I still wouldn’t want to tell you stop by step. Please stay safe, a motor is not worth your life100% with you on that unfortunately my boss makes me do heaps of stuff I know I shouldn’t be doing I pretty much rely on advice and out of work training.
Even is it is 480v supply so be it, I’m more curious to learn how you get 480V in single phase active, neutral and earth, a step up transformer maybe? Note the building does have 3 phase but 3 phase cable is not running to the motor.
That's because you're in the US. In the UK and Australia (where this motor is) 3-phase is 400-415V or more recently 690V for large plant. We normally only use 460-480V split phase in rural locations where heavier loads are in use (e.g. farms) but no 3-phase HV is available. If this looks like a 3-phase motor, you need new spectacles!I’ve never seen a 480vac motor that wasn’t 3phase
Reply to Single phase supply in the Electrical Forum area at ElectriciansForums.net