Dear all. Need to install a generator to power a site cabin. When I test it any idea what I put down as supply type on cert. Never seen 'generator' as an option and its it tt as its under 10kva
Cheers


Sent from my iPhone using Tapatalk
 
Hi,
I quoted for a generator system earlier this year, and the problems were the earthing for generators under 10K could be one of three types.
1 ) Neutral and earth linked at source.
2 ) Floating Earth – Usually frame of generator linked to the earth cable, but no earth as such.
3 ) Earthed centre tapped output (known as V-O-V) which are similar to a three phase supply setup which provide 110V down live AND neutral giving 220V between live and neutral for appliances but only 110V between earth and live or earth and Neutral, however, these generators should never be used to power more than one appliance.

Have a look at the thread “http://www.electriciansforums.co.uk...orum/109155-advice-generator-earthing-2.html” and see if this helps.
 
If you have an earth rod for the generator then I would describe the earthing arrangement for the installation as a TNS system and would note down under other sources of supply "local generator only".
 
Hi thanks for the replays. There is no earth rod. I'm guessing from davidonp's reply it is floating frame so I guess I just note that on NICEIC cert. Cheers


Sent from my iPhone using Tapatalk
 
One more question, what would be an acceptable frequency for retest of the cabin. Bearing in mind it's full of builders I would think monthly but is that overkill ?? ( no pun intended). Cheers


Sent from my iPad using Tapatalk
 
3 ) Earthed centre tapped output (known as V-O-V) which are similar to a three phase supply setup which provide 110V down live AND neutral giving 220V between live and neutral for appliances but only 110V between earth and live or earth and Neutral

Technically there isn't a neutral conductor as no conductor is referenced to Earth. They are both line (phase) conductors.
 

Reply to Site temp generator in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock