Bensen

Hey what kilowatt showers can be feed off 6mm cable and which need 10mm? I guess the distance from the fuse board also needs taking in to account?
 
Hi Bensen, distance plays a big part along with other factors including overcurrent protection and installation methods. I see from your profile that you are a plumber so IMO you should leave electrical cable calcs to the sparks.
 
Meh, it's only a few wires man. What can possibly go wrong?
Apart from a horrible, painful, fiery death.
:)
 
Thanks would many sparks also do the plumbing on an electric shower. Its a swap or a 25year old plus electric shower that has stopped working.
 
considering the last plumber that i last had fit the water supply to a shower... brought it out 2 ft. below where i'd marked the studded wall, so the shower unit would have been only 2ft. above the bath and the cable 2 ft. above the shower, i do my own shower pipework now.
 
Hey what kilowatt showers can be feed off 6mm cable and which need 10mm? I guess the distance from the fuse board also needs taking in to account?

Each shower install would need to be assessed and designed on an individual basis and in accordance with appendix 4 of the regs. The kW rating of the shower and cable length are just 2 of many factors involved. This is definitely a job for someone who has been properly trained in circuit design.
 
Very broadly speaking up to 8.5kw on a 6mm
8.5kw to 10kw will need a 10mm
You need to consider some very important variables including,
The installation method ie is the cable run enclosed in some way or clipped direct.
Is the cable running within some form of insulation ect.
To explain,
The cable under load generates temperatures above ambient, and its ability to dissipate those temperatures will be greatly affected by the way its installed.
You also have to consider the length of run as this can affect the difference between the supply voltage at source and the voltage at the load/shower terminals.
This is known as volt drop and directly relates to the internal resistance of the cable per metre, in relation to its cross sectional area.
The characteristics of the protective device are also important as you need to ensure that the device disconnects the supply before the user of the shower receives an electric shock, should a fault condition develop.
The installations integrity need to be verified to ensure insulation,polarity, along with a low resistance earth return path are able to satisfy these requirements.
A certificate recording these results is produced to provide a paper trail for future reference.
Building regulations under part P also come into play when working in bathrooms as they are known as a special location, and these are divided into various zones for compliance.
If all this makes sense to you and you have the appropriate test equipment and knowledge to use it, then your good to go.
If not, consult a qualified electrician.:icon12:
 
Very broadly speaking up to 8.5kw on a 6mm
8.5kw to 10kw will need a 10mm

You need to consider some very important variables including,
The installation method ie is the cable run enclosed in some way or clipped direct.
Is the cable running within some form of insulation ect.
To explain,
The cable under load generates temperatures above ambient, and its ability to dissipate those temperatures will be greatly affected by the way its installed.
You also have to consider the length of run as this can affect the difference between the supply voltage at source and the voltage at the load/shower terminals.
This is known as volt drop and directly relates to the internal resistance of the cable per metre, in relation to its cross sectional area.
The characteristics of the protective device are also important as you need to ensure that the device disconnects the supply before the user of the shower receives an electric shock, should a fault condition develop.
The installations integrity need to be verified to ensure insulation,polarity, along with a low resistance earth return path are able to satisfy these requirements.
A certificate recording these results is produced to provide a paper trail for future reference.
Building regulations under part P also come into play when working in bathrooms as they are known as a special location, and these are divided into various zones for compliance.
If all this makes sense to you and you have the appropriate test equipment and knowledge to use it, then your good to go.
If not, consult a qualified electrician.:icon12:

You have just given this plumber a green light IMO lol
 
Very broadly speaking up to 8.5kw on a 6mm
8.5kw to 10kw will need a 10mm
You need to consider some very important variables including,
The installation method ie is the cable run enclosed in some way or clipped direct.
Is the cable running within some form of insulation ect.
To explain,
The cable under load generates temperatures above ambient, and its ability to dissipate those temperatures will be greatly affected by the way its installed.
You also have to consider the length of run as this can affect the difference between the supply voltage at source and the voltage at the load/shower terminals.
This is known as volt drop and directly relates to the internal resistance of the cable per metre, in relation to its cross sectional area.
The characteristics of the protective device are also important as you need to ensure that the device disconnects the supply before the user of the shower receives an electric shock, should a fault condition develop.
The installations integrity need to be verified to ensure insulation,polarity, along with a low resistance earth return path are able to satisfy these requirements.
A certificate recording these results is produced to provide a paper trail for future reference.
Building regulations under part P also come into play when working in bathrooms as they are known as a special location, and these are divided into various zones for compliance.
If all this makes sense to you and you have the appropriate test equipment and knowledge to use it, then your good to go.
If not, consult a qualified electrician.:icon12:
Stuff and nonsence :biggrin:
 
Yes please, I also like Mustard.
coming from someone who likes creamflow,:ack2:, that's not a very good advert for colmans.
 
New posts

Reply to Size of shower cable in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock