I have a well pump and motor on it's own meter. I do not have the specs on the motor. It pulls up from about 60' down, at about 45 gpm. And my bill is for about 800 kWh per month. The coop utility power goes out periodically and we want to have a propane generator that I can use to keep my water available and a small milk house heater on when the power goes out. I'm not sure what size to buy. How many watt generator do you think I should buy? Thank you.
 
A 15kva transformer should be fine. I have a well thats 360 feet deep and it has a 5 HP motor in the bottom of the well and it pulls around 7 amps
Thank you.

I have a breaker below the meter. I was going to turn that breaker off, tie in the generator below that breaker, with it's own separate breaker. I would turn off the generator breaker, turn on the main line breaker and go about my business. Then, if the utility power went out, I would go out and turn off the main line breaker, then turn on the generator, and then open the generator breaker to run the well. I would reverse that process when the utility power came back on. If there is something inherently wrong with that proposal, I'm all ears.

Thanks again on the sizing question.
 
The generator and utility feed breaker must be interlocked to meet code. Otherwise by mistake you could feed generator power back into the utility line and electrocute the guy working in the hole in the road. For the generator sizing, you really should try to get some specs on the pump or measure the current.
 
What type of pump is it ? Any chance of a picture of the starter ?
I'm not sure. I've had it replaced several times in the last 21 years. On the second-to-last one, September of 2016, I specifically asked for it to be bumped up since my water right is 45 gpm and I was only pulling 25 gpm. They put in a "Submersible GRUNDFOS Model # 35530-11, 35 gpm, 3450 RPM, 3 HP, 230 Volt, 17 full load amps, intake depth 52', 2" pipe. There has been another one put in since then (about 2 years ago) but I lost the specs on it. It could be the same. I have an email into the guy who did it and he said he'd look, but I haven't heard back. But if we assume the last pump (above) is the same, what do you think?
 
As already mentioned would be surprised if 15KVA could not handle a 3HP pump. Best to start it with no other loads on. A transfer switch is the way to go but remember it needs to be sized for the house max supply, not the generator.....
Any chance you could hire one to try it out as you may well get away with a smaller one. Also, i dont know about the US but propane does limit your choice in the UK, a good second diesel is where i would be looking with an inbuilt tank.
 
As already mentioned would be surprised if 15KVA could not handle a 3HP pump. Best to start it with no other loads on. A transfer switch is the way to go but remember it needs to be sized for the house max supply, not the generator.....
Any chance you could hire one to try it out as you may well get away with a smaller one. Also, i dont know about the US but propane does limit your choice in the UK, a good second diesel is where i would be looking with an inbuilt tank.
Would the house max supply be the twin 30 amp breakers, or what the utility is actually sending to the property? Because I have no idea how big their system is.

The only reason I chose propane is because I have a 1k gallon tank on the property that allows me to fill bottles. And someone told me that propane never goes bad.
 
Would the house max supply be the twin 30 amp breakers, or what the utility is actually sending to the property? Because I have no idea how big their system is.

The only reason I chose propane is because I have a 1k gallon tank on the property that allows me to fill bottles. And someone told me that propane never goes bad.
Sorry, i dont know, you generally size it to the rating of the supply. With what you are wanting it really is an electrician type job. There are a few US sparks here but we are mainly UK.
 
Sorry, i dont know, you generally size it to the rating of the supply. With what you are wanting it really is an electrician type job. There are a few US sparks here but we are mainly UK.
Thanks. I wish I could just get one out here. I'd pay, but apparently they are all too busy building new houses. I guess I'll just continue taking 5 gallon buckets down to the river, breaking the ice and lugging them back up the ice/snow covered slope. Old school.
 
The generator and utility feed breaker must be interlocked to meet code. Otherwise by mistake you could feed generator power back into the utility line and electrocute the guy working in the hole in the road. For the generator sizing, you really should try to get some specs on the pump or measure the current.
Thank you. I don't know how to do that.

I'm not above paying an electrician but I can't seem to find one.
I have to agree with @Lucien that you need a interlock kit or transfer switch because it can be very dangerous if you get confused. Well pumps doesn’t have a starter nor heaters, it’s just a set of contacts that pull in when the pressure switch drops to its desired setting. 45 gallons per minute is a lot of water and you Need to set your pressure switch a little lower which is probably why your motor keeps going out. I’ve had mine 23 years and changed the motor 1 time
 
I have to agree with @Lucien that you need a interlock kit or transfer switch because it can be very dangerous if you get confused. Well pumps doesn’t have a starter nor heaters, it’s just a set of contacts that pull in when the pressure switch drops to its desired setting. 45 gallons per minute is a lot of water and you Need to set your pressure switch a little lower which is probably why your motor keeps going out. I’ve had mine 23 years and changed the motor 1 time
I think I'm still at 35 gpm (even though my water right is 45 gpm). I have/had things set at 40 psi on, and 60 psi off. But I also have a cycle stop valve in the line. Some well people have set that out of the range on the directions in order to give me more pressure due to friction loss far from the well. But I've set it back in range, per the directions, because I seem to have plenty of pressure 2,000 feet away.
 
I think I'm still at 35 gpm (even though my water right is 45 gpm). I have/had things set at 40 psi on, and 60 psi off. But I also have a cycle stop valve in the line. Some well people have set that out of the range on the directions in order to give me more pressure due to friction loss far from the well. But I've set it back in range, per the directions, because I seem to have plenty of pressure 2,000 feet away.
My friends well pumps 27 gallons a minute and they told him that they could supply a whole neighborhood
 

Reply to Sizing a propane standby generator in the USA area at ElectriciansForums.net

Similar Threads

I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
278
I currently have a 100 amp sub panel for a 50 amp RV hookup (on a 60 amp breaker). This is about 100ft from the main with 2/4 wiring. Would a...
Replies
1
Views
908
Another one that some of you may be interested in.......... We had a call to remove 4 off blackstone generators from a pumping station in south...
Replies
3
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
615
Hi all, I've got a small catering business out of a converted horse trailer and purchased an inverter generator to power the trailer, mainly just...
Replies
8
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock