Hi, looking at installing a sub main down to a field to supply caravan hook up points. the supplier has stated they are installing 2 x 100 amp split phase 180 degrees apart. not worked on 460v/480v split phase - my question is how do i go about sizing the neutral. i plan to run a steel wire armoured. i plan to export the 2 phases down the field. does the neutral need to carry both maximum currents, or do the phases effectively cancel each other out requiring a smaller neutral conductor? any help or where to look for guidance is kindly appreciated.
 
The situation is a bit like 3-phase neutral, in that a linear and balanced set of loads lead to zero neutral current, but worst case of full load on only one of the line-neutral sides could lead to the neutral carrying the same current as the supply rating.

Of course reality is likely to be somewhere between the two and it might be possible to use a half-side neutral, but without detailed knowledge of it, and if the cable is not huge singles, then you are probably going to end up using 3-core SWA, or 4-core if a copper CPC is needed for ADS or PME-bonding requirements, so neutral will be the same anyway.
 

Reply to sizing neutral on a split phase 180 deg in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

We have a meter EDMI - ES30B fitted to our property. I understand from the fact sheet for the smart meter...
Replies
13
Views
2K
Greetings, I'm a EE and have installed many electrical systems but am now dealing with my first large 3PH install on our property. I'm not...
Replies
4
Views
864
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
814
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I have a single 7kW EV charger that serves three holiday cottage. The supply to it is E7, with the night rate currently at exactly half the day...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock