Hello all,

I installed an SMA SB4000TL and 16 JA Solar 250 watt panels yesterday as 1 string of 10 and 1 string of 6 as per sunny design 2. The inverter was showing 0v on second string so I rechecked for voltage on open string ends and was getting 214v dc. Plugged strings back in again and still showing 0v on second string but 360v on first string. I have fitted lots and lots of SMA inverters without any issues some I am assuming it is something I have missed or not done properly but does look like some sort of fault in the inverter. I am going back to property in the morning and will ring SMA technical from site but was wondering if anyone else had ever had problems like this with SMA stuff. Ten panel string is in input A and six panel string is input B as per sunny design as well.

Many thanks
 
Also check your connections all the way back to the inverter. If you've got a poorly crimped or applied connector you'll have zero voltage.
 
Will double check polarity in morning but from memory I checked that and it was ok. Connections must be good as at inverter I have voltage on end of sunclix connectors, just none showing on inverter display.
 
Sometimes 6 Panels wont produce enough to 'kick in' inverter hence why the string of ten is working and string of six isnt, You may need to make your strings 8 & 8, as 8 panels produce enough. This has solved similar problems for me in past! Hope it helps.
 
Have you definitely connected 10 on input A, 6 on input B
if they're both into input A you'll only see the voltage from one set of panels and the inverter display will display zero volts/current on the 2nd string ,as you have voltage on the string ends i would think this may be the problem as its an easy mistake to make especially if you've done lots of other installs with both strings into input A and worth double checking
 
Last edited:
Have you definitely connected 10 on input A, 6 on input B
if they're both into input A you'll only see the voltage from one set of panels and the inverter display will display zero volts/current on the 2nd string ,as you have voltage on the string ends i would think this may be the problem as its an easy mistake to make especially if you've done lots of other installs with both strings into input A and worth double checking

Easy one to miss.....
 
Another thing to try is to connect the smaller string of 6 into input A with the string of 10 disconnected ,this will tell you if there is a problem with input B

sorry wstevew already suggested this above
 
Last edited:

Reply to SMA SB4000TL problem in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
807
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
423
At work we've got an 8 panel single string set up, going into a 3000w inverter via a double pole DC isolator. The AC goes supply > isolator >...
Replies
11
Views
3K
TLDR - I have a system that is supposed to have optimisers fitted, but I am not sure they have been fitted. The detail: Back in March I had a...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock