I installed an SMA SB4000TL and 16 JA Solar 250 watt panels yesterday as 1 string of 10 and 1 string of 6 as per sunny design 2. The inverter was showing 0v on second string so I rechecked for voltage on open string ends and was getting 214v dc. Plugged strings back in again and still showing 0v on second string but 360v on first string. I have fitted lots and lots of SMA inverters without any issues some I am assuming it is something I have missed or not done properly but does look like some sort of fault in the inverter. I am going back to property in the morning and will ring SMA technical from site but was wondering if anyone else had ever had problems like this with SMA stuff. Ten panel string is in input A and six panel string is input B as per sunny design as well.
Many thanks
I installed an SMA SB4000TL and 16 JA Solar 250 watt panels yesterday as 1 string of 10 and 1 string of 6 as per sunny design 2. The inverter was showing 0v on second string so I rechecked for voltage on open string ends and was getting 214v dc. Plugged strings back in again and still showing 0v on second string but 360v on first string. I have fitted lots and lots of SMA inverters without any issues some I am assuming it is something I have missed or not done properly but does look like some sort of fault in the inverter. I am going back to property in the morning and will ring SMA technical from site but was wondering if anyone else had ever had problems like this with SMA stuff. Ten panel string is in input A and six panel string is input B as per sunny design as well.