I recently had CCTV installed and the contractor installed a plug socket in my loft, spurred from the lighting circuit - which is unearthed. He added a four-plug extension lead to take the plugs for the four cameras. Is this safe? Or should I be concerned? Many thanks for any advice and help.
Karen
 
I recently had CCTV installed and the contractor installed a plug socket in my loft, spurred from the lighting circuit - which is unearthed. He added a four-plug extension lead to take the plugs for the four cameras. Is this safe? Or should I be concerned? Many thanks for any advice and help.
Karen
Yes you should if what you say is correct, get it looked at by a proper electrician.
Assuming what you say its correct, the reason that the socket is not earthed could be that your lighting circuit wasn't / isn't earthen in the first place, this will be a problem for you as well, I'm certainly not trying to frighten you, you really need to get this issue looked at soonest. Good luck, other people have asked about an electrical certificate, from what you say in your post, that sounds doubtful, who was it that installed your CCTV, an electrical contractor or some Chancer.
 
Last edited:
Sockets, though not banned, should not be put on lighting circuits. Think what would happen if you or your partner plugged a fan heater into the 4 way extension. Total darkness in the loft, panic, and a foot through the ceiling perhaps. As for an unearthed socket the mind boggles.

Get the socket rewired as a spur on the upstairs ring final. You can probably drop the cable down inside or behind a wardrobe or cupboard.
 
As already mentioned, not ideal, you could in theory add a fused connection unit and feed a dedicated socket/appliance from it.
depending on your upstairs walls, you might be able to run a cable to the loft from your upstairs sockets to feed the cameras.
Best advice though is get an electrician in to check this over as it doesn't seem right what you have had done. Ask around for recommendations as thats often the best way to find somebody decent, any chancer can knock up a website or business card
 

Reply to Socket added in loft to lighting circuit - unearthed in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
623
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
645
Hi All, so I have a outdoor cctv camera that you plug in - I'm thinking of attaching this to the soffit and going into the loft from there (very...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock