The answer, I think, is more a practical one than theoretical - at some point you'll run out of allowable Zs!!
From the OSG 4mm on 32A B is limited to 43m on VD (really 86m if loads are evenly distributed, as they probably would be with multiple sockets over a couple of rooms) and potentially much less on Zs (if, like me, you really don't like the idea of depending on the RCD for disconnection). Then it has 28m on TN-S typical max Ze

For comparison a RFC with 2.5mm on 32A B is 106m / 96m

For the OP's original 2.5mm & 20A probably around 84m on VD (distributed load) and 60-70m or so on Zs?
 
Last edited:
Thanks for the information and help, the sockets won't be heavily loaded and not all used at the same time but just to be safe I think i am going to go with the 4mm radial ?
 
If you DID put 500 sockets in, you'd save on cable length...but your wrist would ache from making all the terminations...
and it would be rather more costly
Just been doing a loft extension with a client who really likes sockets.... A child's fairly normal size bedroom with 12 sockets - I think he wanted them near the bed, but couldn't decide where the bed was going!

Also 4 round pin sockets on the light circuit in the master bedroom, while will probably never get used....

I did put in 2 x 20A radials for 4 upstairs bedrooms when I might well have only gone with one in a 'normal' installation.
 
Other than slightly increased initial costs, I can see only benefits to running several circuits where tradition might dictate that one would suffice.

Less inconvenience in the event of a fault. Less time involved in fault finding, should future issues arise. Reduced likelihood of a broken neck when extension leads are used in place of diagnosis and repair...
 
Other than slightly increased initial costs, I can see only benefits to running several circuits where tradition might dictate that one would suffice.

Less inconvenience in the event of a fault. Less time involved in fault finding, should future issues arise. Reduced likelihood of a broken neck when extension leads are used in place of diagnosis and repair...
If AFDDs are required in AMD2 then I can see new builds going back to as few circuits as possible!
 

Reply to Sockets on a radial circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
593
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
932
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Hello all, Trained years ago, not done much for about a decade but I've been asked by a friend to add 5x double sockets into an industrial unit...
Replies
10
Views
1K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock