Quick question which I will probably kick my self when I look into the d/b in the morning.
We currently have a house being restored(finishing touches) had western power out this morning to change over to PME, I came home from work popped in the house to catch the first half of the rugby and put the kettle on.
On the split rcd board down stairs ring and upstairs lights on one rcd, with downstairs lights on the other rcd all running fine until I turned the kettle on which tripped out the rcd with only the downstairs lights on any ideas of what I might be missing by the sockets on the other rcd making it trip with the kettle?
All advice welcome (and laughs)
Presumably it was TT with a high Ra previously?
It sounds like the electrician who fitted the CU did not carry out the testing properly before switching it on!
This is the classic symptom of a neutral to earth fault
So the current would divert from the neutral to the earth, then from the earth to another neutral and then flow through the other RCD causing that RCD to trip while the first RCD doesn't trip?
I think it has all been said above, however the RCD that trips is protecting the circuit on which the fault is present.
Therefore there is a fault on the downstairs lighting.
because the RCD tripped when using a high load on another circuit this indicates that there is a neutral earth fault on the downstairs lighting.
It does not happen all the time because there is only a small percentage of the current flowing through the fault, however any current in use on the installation can cause this because the current can flow from the main switch common neutral back vie the RCD neutral on the faulty side through the NE fault and to earth.
The current flowing through the neutral does not have a corresponding live current and so the RCD trips.
Can you confirm that all the outgoing neutrals have been disconnected from the neutral bar on the RCD that trips...
Switching off the MCB will not affect the fault as it is on the neutral that is not switched off.
You need to find the fault on the lighting circuit and testing of the circuit will do that for you, to some extent.
Little diagram to clarify (or mess up) your approach
EDIT: Just too late fault is found, typical!!:sick:
Reply to Sockets tripping different rccb? in the UK Electrical Forum area at ElectriciansForums.net
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
7K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...