Doing a re-wire for a customer who's had their kitchen redone recently and told me the electrics are fine.when I checked, they've all been wired using 1.0mm 3 core flex then sealed underneath tiles.I can't remove the tiles or pull through new cables.Is it permissable to leave it connected like this and if I do, what max breaker can I use?Can I simply write on the form about the departure from the regs?
 

Marvo

-
Mentor
Arms
Esteemed
How is the circuit protected? Isit a ring or a radial? Maybe it is safe if they've used a 5A MCB. :)
 
E

electrician4u

  • Thread Starter Thread Starter
  • #4
I did metion they're sockets so I don't think a 5A MCB is a serious suggestion.I also mentioned I cannot rip off the tiles so purchasing a scutch chisel would seem somewhat pointless.Any serious suggestions?
 
D

Deleted member 26818

  • Thread Starter Thread Starter
  • #5
Taking into account that there are probably de-rating factors that would apply, most likely 10A.
If there are no de-rating factors, then 16A.
 

Marvo

-
Mentor
Arms
Esteemed
Your questions are somewhat confusing. It doesn't matter that they're sockets, the MCB size is determined by the the CSA of the cable, it's length and the installation method.

My questions are still relevant; is it a radial or ring? How is the circuit protected ie is there an RCD or RCBO?
 

Strima

-
Arms
Esteemed
Best change the MCB for 10A then if your cable calcs allow. If their kitchen has been done by a company I would be recommending that they get them back to do it properly. As they require power then I would run in a circuit that would be suitable in the mean time IF and a big IF they are willing to go for the extra spend.

Did you do a full survey before the rewire and agree and limitations etc with the customer?
 
E

electrician4u

  • Thread Starter Thread Starter
  • #8
they appear to be wired as a ring which i can connect into and i'm changing the CU so would i get away with a 20 A MCB?
 
E

electrician4u

  • Thread Starter Thread Starter
  • #9
I did a limited PIR before but didn't take every socket off the wall.Had no reason to suspect that it had been done in flex.I assume the homeowner either did it himself or a mate of the kitchen fitter did it. either way, it makes it difficult to remedy.
 

Strima

-
Arms
Esteemed
Is there an EIC for the sockets? It would be worth looking at.
 
E

electrician4u

  • Thread Starter Thread Starter
  • #11
you're kidding aren't you.?..it's clearly not been done by an electrician
 

Richard Burns

-
Mentor
Arms
Esteemed
This is certainly an unusual and poor method of installation, however since the ccc of a 1mm flex is 10A (so long as there are no derating factors (which is unlikely) ) then you would be able to have this as a ring on a 20A MCB.
I would tend towards spin's position and use a 16A MCB to allow for the installation methods. This could lead to nuisance tripping, especially in a kitchen, but would meet the requirements of the regulations ( but I would make a note on the certificate). It may be a good idea to, if possible run in another radial for high current appliances like kettles and toasters so that they are off the main ring.
A standard household circuit should be OK on 16A but maybe not a kitchen.
 
D

Deleted member 26818

  • Thread Starter Thread Starter
  • #14
they appear to be wired as a ring which i can connect into and i'm changing the CU so would i get away with a 20 A MCB?
No.
You have cables with a maximum CCC of 10A, that's without any de-rating factors.
You place a 20A load anywhere other than at the mid point of the ring, and you're going to oveload one of the cables.
The maximum you can have is 16A.
 

kingeri

-
Arms
Simple answer is that it needs redoing properly. Customer might not like it, but I'd advise them to get hold of whoever did this and either wring their neck or get the money back.
 
O

Octopus

  • Thread Starter Thread Starter
  • #17
If you know this 1mm core is there and the customer wont agree to remedial work you should simply walk away.

Too much hassle IMHO.
 
E

electrician4u

  • Thread Starter Thread Starter
  • #18
why would a load need to be midway in a ring to avoid overloading??that's the point of a ring, that every point is the same in regards to any load upon it.I find that worrying that someone would think otherwise
 
E

electrician4u

  • Thread Starter Thread Starter
  • #19
I can't walk away from the job.I've already started and ripped most of the (old) cable out.Another example of the customer thinking I'm trying to milk more money out of the job! As far as they're concerned it's a case of it's been working fine since it was put in, so leave it
 
I can't walk away from the job.I've already started and ripped most of the (old) cable out.Another example of the customer thinking I'm trying to milk more money out of the job! As far as they're concerned it's a case of it's been working fine since it was put in, so leave it
Sorry fella but you ARE trying to milk them as this problem should have been spotted and mentioned to them before you started.
people on here are trying to advise your question and it would seem you know better than them as you don't want to accept the replies.
Perhaps they should rewrite the regs for each job you want to do to suit you.
 

snowhead

-
Mentor
Deleted what I wanted to say...

I am speechless....

I'll say it for you,

I can't believe anyone can think leaving the flex in is satisfactory or even complient.
And trying to make a ring out of 1.0mm?
And in a kitchen?

Regardless of what the customer wants or not, it's either a proper job or walk away, even if you've spent money.

This job will come back to haunt you in the future, maybe sooner rather than later.
 
H

Heisenberg

  • Thread Starter Thread Starter
  • #23
I can't believe anyone can think leaving the flex in is satisfactory or even complient.
It is my understanding, and I'm sure that someone will correct me if I'm wrong, is that the fact that flex was used is not the issue here, it's the fact that the CSA is not sufficient.
I had always believed that the reason people use T&E over flex is that flex is much more expensive. As long as the CSA of the cable meets the CCC requirements, surely it does not matter if it is flex or T&E? Am I wrong in thinking this?? Reg No please ?
 
G

Geoffsd

  • Thread Starter Thread Starter
  • #24
That's correct but I'm sure snowhead just meant the flex used here.
 

kingeri

-
Arms
It is my understanding, and I'm sure that someone will correct me if I'm wrong, is that the fact that flex was used is not the issue here, it's the fact that the CSA is not sufficient.
I had always believed that the reason people use T&E over flex is that flex is much more expensive. As long as the CSA of the cable meets the CCC requirements, surely it does not matter if it is flex or T&E? Am I wrong in thinking this?? Reg No please ?
I believe you're right, flex could be used, so long as the CSA is adequate for the job. Could actually be easier to work with, but as you say would be too expensive!
 

snowhead

-
Mentor
It is my understanding, and I'm sure that someone will correct me if I'm wrong, is that the fact that flex was used is not the issue here, it's the fact that the CSA is not sufficient.
I had always believed that the reason people use T&E over flex is that flex is much more expensive. As long as the CSA of the cable meets the CCC requirements, surely it does not matter if it is flex or T&E? Am I wrong in thinking this?? Reg No please ?
To clarify then: "The flex", as in the 1.0mm flex stated by the O.P.
 
G

Geordie Spark

  • Thread Starter Thread Starter
  • #27
Simple answer is that it needs redoing properly. Customer might not like it, but I'd advise them to get hold of whoever did this and either wring their neck or get the money back.
What do you mean either or ?? ..... I would do BOTH !!! :73:
 
G

Geordie Spark

  • Thread Starter Thread Starter
  • #29
There is a possible benefit in leaving this 1mm flex in place & that is during winter time it could supplement the underfloor electric heating. :)

every cloud etc. ..............
 

Strima

-
Arms
Esteemed
Is it me or are there no de-rating factors for flex, or have I gone blind...

Is the stuff not designed to be free in air and only have some minor weight bearing capability for supporting lamp holders etc...

Or am I talking complete bollox...
 
G

Geordie Spark

  • Thread Starter Thread Starter
  • #33
Is it me or are there no de-rating factors for flex, or have I gone blind...

Is the stuff not designed to be free in air and only have some minor weight bearing capability for supporting lamp holders etc...

Or am I talking complete bollox...
It's also useful for lashing stuff to the roof rack.
 
Is it me or are there no de-rating factors for flex, or have I gone blind...

Is the stuff not designed to be free in air and only have some minor weight bearing capability for supporting lamp holders etc...

Or am I talking complete bollox...
Would it not be prudent to apply some derating though? If something can carry 10 amps but is thenfor example, buried under a mountain of tickly wool it's going to have an effect on it
 

Strima

-
Arms
Esteemed
Would it not be prudent to apply some derating though? If something can carry 10 amps but is thenfor example, buried under a mountain of tickly wool it's going to have an effect on it
Very true, I would use the trusty 0.5 method just to be sure. But serious question, are there any installation methods/factors for flex?
 
There's nothing to say you can't hard wire in flex, there was a long thread about it a few months back and the general concensus was that it's acceptable. You just wouldn't though, would you?
 
O

Octopus

  • Thread Starter Thread Starter
  • #38
There's nothing to say you can't hard wire in flex, there was a long thread about it a few months back and the general concensus was that it's acceptable. You just wouldn't though, would you?
especially if IT IS 1.0mm on a 32A breaker
 
especially if IT IS 1.0mm on a 32A breaker
Like Geordie said though, the tiles will be warm in winter when wiping over to keep them clean. Well it's only a few wires man, what can possibly go wrong?
Apart from a horrible, painful, fiery death.
:)
 

Strima

-
Arms
Esteemed
Flex has it's place, I'll leave it at that... :lol:

I would be pressuring the client to get the original installer back to rectify the sockets free of charge, why should the client pay for bad work?
 

Reply to sockets wired in 1.0mm 3 core flex in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Top Bottom