Any help on solar array swa sizing? 4kw array needed around 20M swa from house to array.
thanks
thanks
Discuss Solar Array swa sizing in the UK Electrical Forum area at ElectriciansForums.net
I guess if the inverter is periodically altering the drive current / phase angle and monitoring its terminal voltages then it could determine the supply impedance rather like a MFT does Zs, etc. True, that is not measuring just the feed cable but the whole network, but I guess in most cases the supply impedance (i.e. leading to PSCC) from the 60-100A grid is going to be far lower than the end of sub-main for a 10-20A feed.I have never got my head around how the inverter can see the volt drop and then add to it , but apparently it does .
Is your question regarding the 230V ac or the direct current produced by the 4kW array; I read your question as the latter.Any help on solar array swa sizing? 4kw array needed around 20M swa from house to array.
thanks
Electricity cost | 27.9 | p/kWh | | | |
Solar power (max) | 4 | kW | | | |
Solar max current | 17.4 | A | | | |
Solar average/max for I2R | 0.25 | (ratio) | | | |
Solar average power | 1 | kW | | | |
Solar average current | 4.35 | A | | | |
Expected lifetime | 20 | years | | | |
Cable length | 20 | m | | | |
Cable size | 2.5mm | 4mm | 6mm | 10mm | |
Resistance | 14.8 | 9.2 | 6.2 | 3.7 | Ohm/km |
Loss | 5.60 | 3.48 | 2.34 | 1.40 | W |
Lost annual power | 47.8 | 29.7 | 20.0 | 12.0 | kWh/year |
Annual cost | 13.3 | 8.3 | 5.6 | 3.3 | £/year |
Over lifetime | 267.0 | 165.9 | 111.8 | 66.7 | £ |
Volt drop (max) | 5.15 | 3.20 | 2.16 | 1.29 | V |
Volt drop (max %) | 2.24 | 1.39 | 0.94 | 0.56 | % |
Cable size | 2.5mm | 4mm | 6mm | 10mm | 16mm | |
Resistance (per unit length) | 14.8 | 9.2 | 6.2 | 3.7 | 2.3 | Ohm/km |
Resistance (installed) | 0.296 | 0.184 | 0.124 | 0.074 | 0.046 | Ohm |
Loss power | 5.60 | 3.48 | 2.34 | 1.40 | 0.87 | W |
Lost annual energy | 47.8 | 29.7 | 20.0 | 12.0 | 7.4 | kWh/year |
Annual cost | 13.3 | 8.3 | 5.6 | 3.3 | 2.1 | £/year |
Over lifetime | £266.95 | £165.94 | £111.83 | £66.74 | £41.49 | |
Volt drop (max) | 5.15 | 3.20 | 2.16 | 1.29 | 0.80 | V |
Volt drop (max %) | 2.24 | 1.39 | 0.94 | 0.56 | 0.35 | % |
Cable cost (per unit) | £1.74 | £2.36 | £3.08 | £4.75 | £7.09 | £/m (Superlec LSZH Apr 2022) |
Cable cost (installed) | £34.80 | £47.20 | £61.60 | £95.00 | £141.80 | |
Total cost (cable + loss) | £301.75 | £213.14 | £173.43 | £161.74 | £183.29 | |
There are on line estimating tools which can produce annual and month by month figures for pv generation.I may have really over-estimated the average solar power, but equally I have probably underestimated future electricity costs as well but a large amount!
I have seen some tools such as that and they offer you the expected annual power. But the problem here is the I2R losses depend on the current squared, so the shape of the illumination waveform has an impact on the relationship between average solar generation and average cable loss.There are on line estimating tools which can produce annual and month by month figures for pv generation.
Reply to Solar Array swa sizing in the UK Electrical Forum area at ElectriciansForums.net