Phantasmagoric

can anyone confirm does the containment on the d/c side of the p.v installation need earthing as per norm.reason im asking is someone at work mentioned it should be left not earthed which i find a little hard to believe.
 
Transformered inverters are class 2 devices so the DC side is galvanically isolated from the AC no need for earth. If you use a transfomerless inverter (more efficient) then you need to earth the frame and thats easy for TNS but any PEN system requires a separate earth spike. Avoid TL inverters I say and don't earth.
 

Reply to solar p.v containment earthing in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock