come on all of you some one must know ?
I posted this 5 days ago and no answers yet !!
what does every one else write down on the certs ?

Hi all
i would like to know how to calculate MAX DEMAND for the certificates ?
i've tried the diversity calculaters in the book but found in a normal house with 2x rings, 2x lights, cooker,shower or two etc. they always come out too high. if some knows the correct formular i could write a little prog and post it for others to try :)
 
Use one of these at the tails with loads on the circuits.
Megger MMC850 Multi Single Core AC Clamp Meter

Or as you are already doing, use the osg.

Dont take rings as 32A, use some common sense & calculate what will be applied as a load to the circuit (upstairs ring final will have a lesser load than the kitchen or downstairs ring final).

Use diversity on the lighting circuits.
Use diversity on cooker/oven circuits

Showers well use potential full load.
 
i record the max demand the same as the main protective device for the cu in question,because that is the maximum it can pull,
however i know this is not 100% correct but as you have seen from the lack off replys to your post it seems to be a grey area. cheers
 
I put maximum demand down to the largest MCB in the board. Never been picked up on my assessment yet.

But then you could always out down the cutout rating as its unlikely it will pull much above that.
 

Reply to some one must know ??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
978
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
707
Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
797
Its time I bit the bullet and got some proper certification software, I've used my own forms for ages now which I spend pre-filling everything in...
Replies
8
Views
1K
Hi, I'm new here so apologies if this isn't the correct area to post this. We moved in to a bungalow around 8 months ago and had a full re-wire...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock