For £40 I’d rather just fit it than bother doing the calculation/rail assessment ?
in my own house, i probably wouldn't bother.
at a customers place, why wouldn't you?
£50 on the price of the job, 30 to 40 on the cost of materials. quid's in??
the last thing you want is a customer coming back to you in 10 months time saying that all there tv's and computers have gone bang and they cant understand why because they have an up to date electrical installation and thought it should protect there equipment.
right or wrong, it is an argument that you don't need to have.
Yeah I’m getting this idea too but it’s like the chances of that happening are very slim don’t you think? Will probably just fit in anyway
[automerge]1596230261[/automerge]
Or I would ask 'How many appliance faults have been caused by surges over the years?'
Will never know if it just becomes faulty on its own or if it’s surged
[automerge]1596230330[/automerge]
I am going for the clever marketing theory.
Not seen many things damaged by a surge.
Seen stuff destroyed by lightning, spd not going to protect against that.
Seen stuff damaged by loss of neutral, not sure if spd could protect against prolonged overvoltage.
Oh I thought it actually protects from lightning / power loss / voltage disturbance
[automerge]1596230550[/automerge]
You don't have to fit an SPD in a single dwelling unit. You don't need to do a risk assessment
It might be a good idea to fit one, depending on cost.
The problem I have is I really like to fit Hager consumer units. I don't know if its the same for everyone, but adding an SPD is costing me more like £80 extra so I tend not to as the customers are not keen on that much extra cost.
This is exactly my dilemma. I’m going for a Hager split rcd board. The spd is about £80. I know this might sound wrong but should I just include the spd as part of the consumer unit material cost without mentioning the spd itself? The customer will more than likely be like ahh nah leave that then I’ll be thinking I should fit it then it’ll be like a debate about an spd which “Might” save their appliances. You know how it goes. “If it works, don’t worry about it” the client will say lol :rolleyes:
But you don't know that. It's often difficult to prove what actually causes equipment to fail.
That’s right and I guess it’s a risk if I don’t fit it. I’ll just fit it
[automerge]1596230708[/automerge]
How do you know how many appliances have become faulty because of a voltage spike?
I don’t and I guess that’s a risk I won’t take by not fitting a spd.
[automerge]1596230854[/automerge]
How much failed electronic equipment have you actually looked at in detail to establish the cause of it being damaged?
As for knowing of other people having seen it, it's not exactly going to be the first thing your friends tell you about when you speak to them.
In my life I've known of quite a few appliances stop working for no apparent reason and never bothered to find out why, just replaced them and carried on. TVs, microwaves, boiler programmers, the clock in gas cookers, countless phone chargers.
I guess then, once the spd is fitted, if it gets knackered and needs to be replaced, this would of probably saved an appliance or more
[automerge]1596231498[/automerge]
I’m having a look at Hager boards split rcd online with the fitted spd. I’m putting in 9 circuits so will want 3 ways free to come to the next available amount of ways Hager would offer which would be 12 way. But if I saw a board which said 12 way split rcd with spd. Does this mean I have an actual 12 ways for 12 mcbs to be used? Or would the spd take 2 of the ways leaving me with 10 ways (1 spare)? If you could pm me please
Get something like this, factory fitted spd and twelve ways for rcbos.
For a 12 way consumer unit, that would add nearly £200 to my price.
I usually fit high integrity, with 2/3 RCBO’s
I’m paying slightly less than £100 on that board. Deals to be had if you shop around. Hager SPDs on their own we are paying mid£60 for. Look after your wholesalers and they’ll look after you ?
Why the dislike on my post @richy3333 ?
What’s the price difference you are getting between 10 way high integrity with 8mcbs and the same but with SPD also.
The difference is around £80 whichever wholesaler I speak to
I disliked your post and your previous one on the other thread because its my view that your reading of the regs is not correct regarding the fitting of SPD's in a domestic situation. We dont even give the customer a choice, we just explain what they are and why we are fitting them. If customers are that penny pinching over an SPD then they aren't my customer (we aren't bottom feeders - not suggesting you are either BTW).
Regarding CU's I have fitted only 1 or 2 high integrity boards in the last 8 years. We only fit Hager RCBO boards or (presently) fusebox RCBO if the client needs cheaper; but we normally sell them Hager. We fit Hager 3PH also. We do at least a board change a week, 2 this week and all Hager RCBO's. We literally buy 100's of RCBO's a year. Its now made good for us with the Hager points rewards.
That's all well and good, but it still doesn't mean an SPD has to be fitted.
The regs say its not required and no risk assessment is needed. Your personal opinion might be different, but that is what it says in black and white.
Nearly all my customers choose not to pay the £80 extra for an SPD. I'm not going to fit one out of my own pocket. I'd rather £80 in my pocket than Hager's.
I'd like to fit RCBO's on all circuits. In reality it's simply not necessary for most houses with an installation in good condition. I fit them on circuits supplying anything outdoors and ground floor sockets that might be used outdoors/supply kitchen appliances. These cover 99% of RCD trip instances imo.
I have a sign in my van that reminds me, business first, electrician second.
Hi @mattg4321 its not personal opinion but interpretation of the regs. There are members on here with far more knowledge and experience than me that agree. Industry ambassadors (like the E5 group or GSH, Efixx et al) also feel the same.
I've not suggested you should pay for the device out of your own pocket?
I dont agree that RCBO boards are 'simply not necessary' when you take into account earth leakage, DC leakage of equipment, devision of circuits, inconvenience and functionality of the installation. Theres industry talk that split load boards could be phased out in coming years so that doesn't really support your stance. I would be failing my customers and also the regs by just fitting a split load board without proper consideration at the design stage of a wire/rewire/board change. Do you not discuss these factors with your customers so they can make an informed decision?
We have differing views on the matter of SPD's and clearly different USP's/models with regards to running our own businesses so I dont see us coming to any collective agreement, but will respect your position.
I think you may be reading the wrong regs book.
This basically means that:
If the risk assessment is not performed SPDs must be fitted except for single dwelling units where the total value of the installation and equipment therein does not justify such protection.
This means that you can perform a risk assessment to establish whether SPDs are needed or, for single dwelling units, you can effectively do a cost/benefit analysis.
You need to consider the value of the installation and equipment. For this analysis you could start with the purely financial value:
What is the financial value of the parts of the installation that could be damaged by a surge, the cost of all RCDs, RCBO's, USB sockets, LED lights and their drivers, central heating controls, boiler PCB.
Then add this to the financial value of all the equipment in the installation which could be damaged by a surge, so TV, radio, phone chargers, some appliances.
Add this together and compare it to the cost of installing an SPD.
So if the replacement value of everything that could be damaged by a surge is say, a few hundred pounds you could argue that it isn't worth the £80 SPD.
But if it is getting on for £1k or more, the £80 SPD becomes a no brainer.
Of course this reg doesn't specify financial value, just value, so you need to factor in other things like the cost of being without a piece of equipment. So if someone works from home using a computer connected to the Internet, which is quite a lot of people in the current situation what value is that equipment if lost due to a surge?
I read it as a statement of fact not a question.
There is no doubt that using your method means that every dwelling would need an SPD. If that’s the case thenjust make it mandatory? Why is there no need for a risk assessment even?
I’d rather it was made mandatory to save the confusion personally.
The guidance I got from the NIC was to ask the customer. What good is that? How are they meant to make a decision when even we are struggling to?
Im reading the correct regs book. Tell me where it says that an SPD is required? It’s very poorly worded and open to wide interpretation, but it certainly doesn’t say an SPD is required in a single unit dwelling.
In the first paragraph after the list of places where SPDs areandatory in the picture I posted.
It is not poorly worded or open to wide interpretation.
It says, quite clearly, that there is an exception for single dwelling units where the value of the installation and equipment therein does not justify the protection.
This does not mean that all single dwelling units are exempt, it means that only single dwelling units where the value of the protected installation and equipment does not justify the installation of an SPD.
This means that you must assess the value of the installation and use this to establish whether it justifies the installation of an SPD.
Have to agree with you. The regs are not written in very good English, and often leaves things open to interpretation. 'Except for single dwelling, where the total value of the installation and equipment therein, does not justify such protection', IMO does not suggest you carry out a pound for pound calculation or subtraction. Its merely stating, they would not be considered necessary.
But I get the argument, that as they are relatively cheap, compared to say AFDD's, it doesn't make sense not to fit them. But I expect, new cheaper domestic, like social housing (perhaps), they would not be specified.
I really respect your opinion Dave, but nowhere does it say you have to try and determine the value of the installation.
It gives no guidelines as to how this is even done. We’re all filling in the blanks. You’ve come up with a procedure for working out whether or not SPD’s are required, but the reality is that they are not required and no evidence is required that you have put any thought whatsoever into why they are not required.
In my opinion the chances of home working being disrupted are far greater through things like power cuts and ISP service dropouts, yet we don’t go around suggesting generators and UPS’ etc
I like seeing these issues thrashed out, but can't help wondering about situations where including surge protection is less straightforward.
Thinking specifically about tails being in excess of 1m, where a separate unit would have to be installed closer to the cut out or a TT installation that required type 1&2 protection (which seems to limit options and considerably increase cost). Would those who automatically include an SPD in every installation quote for whatever was necessary or would the additional cost mean that these situations might first be discussed with the customer?
Actually they are, for the most part, written in very good English with a high level of technical accuracy.
The problem is often people not understanding technically correct English.
Words like 'should' have a specific meaning in such documents but a lot of people fail to understand this and tend to assume the common, but technically incorrect, usage.
Interpretation is also required yes, in the same way that all rules, regulations and laws require interpretation for use in the real world. This does mean they are open to interpretation or that we are free to interpret them in whatever way suits our own opinions.
[automerge]1596292254[/automerge]
It doesn't say exactly that no, it says that they are not required where the value of the protected installation does not justify it.
How do you know whether the value justifies it without knowing the value in the first place?
Sometimes it will be obvious, sometimes not. It is obvious somewhere such as my grandparents house it wouldn't be justified, the small number of susceptible appliances is obvious.
My sister's house however has half a dozen games consoles, big TV and countless other gadgets permanently plugged in, surge protection would be justified.
The Regulations dont give guidelines on how to do things, they set out the requirements. Regulations are not how to do it books!
The regulations dont give guidelines on how to join two bits of trunking together or how to fix them to the wall, they just set out the requirements that must be met for those processes.
No evidence is required for a great many regulations. No evidence is required to prove that you calculated cable sizes correctly, no evidence is required to support any of your installation design decisions. It doesn't mean that you can just ignore any part of the regulations though.
I seem to have a problem justifying SPD’s to my customers as when I mention them as an option at a cost of £80, I invariably get the response that they have never had a problem with appliances failing etc so don’t see the need.
When we are looking at what size cables to use there are various tables and formulae to use, all within a fairly precise framework. We are not told to simply ‘select the correct size cable’. We follow a procedure to reach a decision.
When deciding whether or not to fit an SPD in a single unit dwelling, there is no such procedure. Are we to go around totting up the value of customers appliances before we reach a decision? Better not forget the cupboard under the stairs where there could be some valuable appliances boxed up that might be plugged in at some point.
Not fitting an SPD doesn’t mean someone has ‘ignored the regulations’. You yourself just agreed that they don’t mandate the fitting of an SPD in a single unit dwelling. We are to decide with no guidance whether or not we can justify fitting one.
If I was of the opinion that I didn’t need an SPD as I’d never had an appliance go wrong in say 50 years at the same address, how could I possibly justify fitting one now? Especially given it is not really an issue of safety.
This particular regulation is a total mess.
Reply to SPD’s in dwellings. in the UK Electrical Forum area at ElectriciansForums.net
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
4K
Hi, I'm installing a new circuit in domestic dwellings for various housing associations my question is do I need to fit an SPD or would it be the...
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
10K