If I was of the opinion that I didn’t need an SPD as I’d never had an appliance go wrong in say 50 years at the same address, how could I possibly justify fitting one now? Especially given it is not really an issue of safety.

This particular regulation is a total mess.

I've never died of an electric shock so I don't need RCDs.

It is not a total mess, it is very clear and straightforward.

I'm sure if you look for it there will be guidance, the IET love to keep publishing guidance notes to accompany the regulations.
 
I seem to have a problem justifying SPD’s to my customers as when I mention them as an option at a cost of £80, I invariably get the response that they have never had a problem with appliances failing etc so don’t see the need.
Probably the same folk who have paid £30 or more for a surge-protection block for their PC, another for their TV, etc.

I get your point that it has not been past practice and the regulations do not make it mandatory, but with the increasing use of LED lighting and all sorts of "smart" devices (a rant for another day...) make them highly desirable to anyone who understands the trade-off.

I guess that is an issue for engaging the customer, but various folk (above) have decided the easiest path to doing things in a way they believe is correct is not to ask and just to included it as part of the normal service.

Asking folk is often not as productive as you might hope, just look at elections!
 
@pc1966 I think @davesparks has made the issue far clearer than I could have said in his recent posts. The regs dont use words like 'mandatory' or 'desirable', they cant as they are not an Statutory Instrument but the use of the phraseology 'shall be' is clear enough.

As for surge protection blocks - extension leads i.e. thats a debate for another day, particularly if different manufacturers are being used :tearsofjoy:
 
"Except for single dwelling, where the total value of the installation and equipment therein, does not justify such protection',"

That is not an instruction to determine a requirement but a statement that the determination has been made and there is no requirement.

Typically poor language.

I fit SPDs because I'm a coward.
 
I've never died of an electric shock so I don't need RCDs.

It is not a total mess, it is very clear and straightforward.

I'm sure if you look for it there will be guidance, the IET love to keep publishing guidance notes to accompany the regulations.

Think you’re perhaps being a little disingenuous here.

RCD’s are a safety issue. We should err on the side of caution. SPD’s are not.

Calling this particular regulation clear and straightforward is akin to saying Boris and his chums have given clear and straightforward advice!
 
Actually they are, for the most part, written in very good English with a high level of technical accuracy.
The problem is often people not understanding technically correct English.

Words like 'should' have a specific meaning in such documents but a lot of people fail to understand this and tend to assume the common, but technically incorrect, usage.

Interpretation is also required yes, in the same way that all rules, regulations and laws require interpretation for use in the real world. This does mean they are open to interpretation or that we are free to interpret them in whatever way suits our own

Disagree. Unlike the text in law written in criminal & civil law offences, documents like BS7671 hardly ever get challenged. Whilst its a technical document, it also tells how certain things should be done, as in this regulation. It even gives us here, a formulae to work out the calculated risk level. However, in the case of single dwelling units, it gives no clear method of calculation. In a criminal law offense, in court this sort of thing is challenged, and the wording of the offense evolves over time.

Like in 421.1.201 (back in 2015), we've had many debates over 'similar switchgear assemblies'. In 5 years, and the debate over that phrase (Google it and see the disagreement), you think they could of given some more clarity for those three words.
 
"Except for single dwelling, where the total value of the installation and equipment therein, does not justify such protection',"

That is not an instruction to determine a requirement but a statement that the determination has been made and there is no requirement.

Typically poor language.

I fit SPDs because I'm a coward.

The critical word is 'where' as in "where the total value..."

'Where' can be used as a conditional adverb, pronoun or conjuction. Without knowing the authors intent it is open to interpretation and in a de facto statutory document that is not good enough.

Had this statement been meant as an instruction to make an assessment of value they should have used 'if' instead of 'where' and provided an example, or guidance, of how this determination should be made.

It is a very good example of subjective reality where the reader has a set of opinions that form their decision making subconsciously.
 
Here's a thought for those who "fit an SPD regardless" ...
Do you also insist on routing the phone line, TV aerial, and any other external service via the CU and fit an SPD in those services as well ? No ? Well your SPD in the CU is going to do diddly squat against lightning induced surges :rolleyes:
Also, the SPD isn't going to protect against a lost neutral - with the let through energy required to control the L-N voltage in that scenario, the overcurrent protection for the SPD will trip, or some internal protection in the SPD will trip/blow, or the SPD is self combust. Think about it, say it needs to pass 10A to hold the L-N voltage down to 240V, it's going to be dissipating around 2.4kW - in a tiny plastic package with limited cooling.
So we're fitting an SPD that isn't going to protect against lightning induced surges, isn't going to protect against a lost neutral and the associated over voltage. Seems like very good value for money then.

Now, a bit more on that first para ...
I do have first hand experience of what lightning can do to stuff - I've experience of sitting down with a pile of new serial port cards to fit in the PCs, stacking a pile of monitors on a pallet to go off for repairs, and going out to the bosses house to replace the fax yet again. These are the only failures I could attribute to surges. None of them would have been helped in the slightest by an SPD as required by the regs.
Surge protection, and it's related science of interference control, is a whole subject in itself and I know enough to know how much I don't know.
Lets start with the simple one - the fax (and answering machine, and cordless phone, and ...) at the bosses house. Common factor ? Connected to both mains and phone line - the services coming from different directions on overhead lines, i.e. the perfect setup for such problems. An SPD in the CU would make diddly squat difference.
Firstly, the impedance of the earthing conductor at the frequencies implied by the rise time of a lightning induced surge is high - we talk about the problems of a high impedance earth rod for a TT supply, this is a similar problem, the impedance of even a few meters of 16mm2 earthing conductor will be high enough to render the SPD ineffective. And of course, for a TN-S or TN-C-S supply, our earth comes in along the same cable as the supply so will pick up surges along with the L & N conductors.
If the surge comes in along the phone line, then the SPD in the CU will do diddly squat.
So in either case, the effect on the differential voltage these sorts of device connected between different services is minimal - and it's that which kills equipment.
You can ONLY protect against that sort of thing by routing ALL the incoming services via one point. I really do mean ALL - that's the lecky, the phone, the TV aerial, the satellite dish cables, cable TV/internet if you have that. The all have to route via one point, so you can fit SPDs to all of them, and have those SPDs share a single common grounding point - the main thing being that they have to be tied together solidly, like being bolted to one bit of copper bar. A few feet of bonding cable will seriously reduce the effectiveness. Doing it this way, the entire installation will share a common equipotential zone - we're familiar with those and the reason for them aren't we ? - even if that equipontial zone pops up to a few kV for a few microseconds. As I said, running a bonding cable across the house to where the phone lines comes in won't help - it'll be open circuit to the sort of signals we are trying to protect against.

A surge protector socket strip is a similar proposition - but only for the equipment plugged into it, and only if all connections to the equipment pass via it. So that means the phone line for modem/internet and network cable. but just having that surge protected socket strip connected properly may "export" the problem to other equipment in the house - remember it's "earth" connection is high impedance to the problem signals.
This "thick cable is high impedance" issue has been demonstrated to me, and I do vaguely recall the theory behind it from uni and other interests in electronics. Specifically when I started work, as an apprentice we had loads of demos etc - you know the routine, how not to kill yourself (or others) on company premises, how not to burn the place down, etc. One was related to EMC (electromagnetic compatibility). In this case they had an expensive military grade filter mounted on military shock mounts to a sheet of metal. Connected through this filter was a small DC motor. Motor on, amplifier connected to supply picks up the interference for all to hear. Filter is connected to metal sheet by about a foot of thick braided cable - think the earthing strap on the car engine designed to take all the starting current. Yup, the filter is ineffective due to the impedance of this short cable. Instructor presses the filter to flex the mounts till the mounting bolts touch the metal sheet - noise disappears.

Oh yes, those serial cards and terminals. This goes back to one of my previous employers, though at the time I (with some colleagues) provided IT services to them. They had a lightning strike not very far from the site - from the description maybe 1/4 mile away across the fields. This created massive earth potential differences - even within one building. At the time nearly everything was "character based terminals connected via serial lines" to a central system - RS232 is designed for +/-25V and takes a dislike to "much higher" voltages fed into it. Each piece of kit had it's own earth potential determined by the local mains earth - with signals coming from another piece of kit with a different mains earth reference. Even stuff connected to the same DB got affected, but mostly it was case of the further away, the more likely to be damaged - and not a single serial port survived by the time the equipment was the other side of the main building. Note that in this one building, one single mains incomer, submains to DBs dotted around the building. The other building shared the same substation (we had our own in the back yard) and no serial links survived there.
Luckily this was back when serial ports weren't integrated onto motherboards, so it mostly just blew the port and we stuck a new card in. The terminals mostly just sacrificed the serial driver & receiver chips which effectively acted as fuses and saved the rest of the electronics. The central system had 64 ports in 4 blocks of 16 - 2 internal cards, one of which survived, 2 external modules, neither of which survived (but the British manufacturer amazingly repaired them FoC).

Having a bit of knowledge on the subject, excuse me if I don't share the enthusiasm for SPDs - like the freestanding socket strip versions, can be of use if used properly, but mostly are a triumph of marketing over facts. I'd also say that if you are paying £80 for an SPD, then you're being ripped off.

If you have trouble getting to sleep, or if you are genuinely interested in the physics, then I suggest a read of BEAMA Guide to Surge Protection Devices (SPDs): selection, application and theory
It dates from 2014, so not exactly a new topic. BTW, I do disagree with some of the details - specifically where they show services entering the building from different directions where (as in the bosses house mentioned above) it's "very difficult" to get low impedance equipotential bonding across all the SPDs.
 

Reply to SPD’s in dwellings. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock