Discuss Split Phase or 3 Phase in the UK Electrical Forum area at ElectriciansForums.net
G
Gasmeter65
Hi, i am rewiring a triple garage with 1st floor into a holiday cottage.
The existing property already has 2x 8.5kw showers and cottage to also have 8.5kw min shower. Also oncludes 3 cookers approx 4kw so with lights n skts approx 40 KW MAX. (over estimating it )
As this exceeds the main single phase CU rating.
( 1 half of the house is a flat with separate DB for shower cooker lights n sockets. i was thinking 3 phase as to have each DB on each phase))
The options are split or 3 phase. Has anyone come across the split phase in a domestic and if so approx costs of each.
Supply is overhead PME max length of cable 20mtrs.
Cheers
When you say 'split phase' are you talking about 180 degree split phase supply or do you mean 2 phases and neutral from a standard DNO 3-phase supply transformer?
I’ve given up even trying to explain 230-0-230/460V transformers. If it was 180° phase shift the line to line voltage would be 0V and the neutral conductor twice the size of the line.
Study transformer vector angles.
i dont want a transformer unless thats what the energy supplier is gonna fit !!
The hot water is going to be heated via a ROINTE and also 3 x wall heater aprrox 1kw each.
Im sure its gonna have to be 3 phase as its near 40kw
just waitng to hear back from supplier. just wondered about costs not a lecture lmfao
I always thought the 180 was relative to the centre point?
I asked because you did not mention these loads in the OP - wouldn't a CH system be better, combi perhaps inc shower provision? (assuming of course gas is option)
the garage is 10 ft away from property, so didnt consider that.
good angle to come from there thanks, but worth asking plumber if its possible.
In practice it might not make much difference if the DB's and loads are all SP+N, only a matter of how the circuits are shared between the DB's. For the same total power, you can get more flexible diversity with the loads divided into two groups rather than three, OTOH 3P is more useful for other purposes which split phase isn't. If there is 3P in the area, that would be my choice. If the HV is SP, then you will be stuck with split.
Luckily there's a telegraph pole 10mtrs from property. Which also supplies the pub 2 doors away :)
Just trying to get some other ideas, hopefully the CH may be a cheaper option as long as boiler is capable
It’s the relationship between the secondary windings and the primary. Primary being 0°.
A standard DNO 3Ph transformer is vector group Dyn11 because red secondary leads red primary by 30° or the 11 o’clock position.
Doh, just re-read this. CH is via Oil n its 40ft away. I was thinking running off existing CH!!
Although it could be an alternative option :)
I am on about something like this:
Yes that's a better pic
You will notice the secondary has current flow in alternate directions - so 180 between each phase split (line) and centre point
You don't use curent flow, you use vectors. It's standard practice.
Only in this type of transformer that confusion arrises.
PS the drawing won't be here long, I'll remove it before I go to bed.
I'm wondering how many of the Electrical Trainee reading this got to Tony's '180deg phase shift' line and then moved directly to the 'which work boots' thread... :)
Reply to Split Phase or 3 Phase in the UK Electrical Forum area at ElectriciansForums.net
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Hi - first-time post from a complete novice. I want to install a 24kw electric boiler on my property but that size requires Phase 3 supply...
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...