I am after a bit of advice for a job I am quoting.

The current set up is 2 workshops next to each other. Both units are fed by 1 2x5x5 split load board. Each workshop has a socket Circuit, couple of heaters and a lighting circuit. No issues there.

The landlord is now renting each workshop out to seperate businesses and wants to bill them seperatly. So my plan is for unit 1 to have the current split load board. Off this (non RCD) a submain circuit for a new RCBO board for unit 2 via a MID Approved Check Meter which can then be billed as necessary.

My issue here is the board is fed in 16mm T&E cable buried less than 50mm in the wall. So needs an upfront RCD. I'm not keen on 2 workshops running off 1 30mA RCD thats in accessible. A 100mA Type S crossed my mind but obviously I need 30mA to protect the submain.

Is everyone in agreement that a new submain with a upfront Wylex 80A Switch fuse is the best Option? This will probably go down like a sack of poop due to costs but I can't see any way around it?
 
Split the supply between dno meter and current db
Run into 2 meters.
Mater A supplying current board
MeterB supplying new board in second workshop.

Alternatively if all party’s are happy, identify the circuits going to second workshop and run all the live conductors for them through the same ct coil that is fed to a meter?
 
Thanks for your suggestion. I did think a Ct coil, but I think all parties would prefer there own mains board.

I think splitting the supply at the DNO point I to 2 meters and then a submain out to each board via a Switch Fuse is the best way. Its just the cost of it the landlord won't be happy with.

My main headach to get it done within their cost is this submain buried less than 50mn in the wall needs 30mA RCD protection, unless anyone can think of a reason why not. It currently doesn't have it even though it was only wired up 5 years ago.
 
My main headach to get it done within their cost is this submain buried less than 50mm in the wall needs 30mA RCD protection, unless anyone can think of a reason why not. It currently doesn't have it even though it was only wired up 5 years ago.
Hi - I may be misunderstanding, but if you don’t touch the existing sub main you aren’t required to fix the “cable in walls” problem its got.
 
if you are using the existing 16mm T/E buried in the wall , there's no requirement to RCD protect it, although current regs demamd compliance with 522.6.204 BYB. Amd.3. (not got 18th). if it's a short buried<50mm, could you cap over with some 2mm steel plate?
 
i'm thinking that as the regs. are not retrospective, you are not obliged to make existing parts of the installation compliant with current edition. as such, a comment on your EIC as a departure should cover it.
 
Cheers tel.

Its just with me changing the switch fuse up front I want the whole installation covered.

I popped there on my way in this morning. Identified the exact route white was about 3.5m. The landlord is happy for a length of 2x2 metal trunking to go over the top of the run. I can then put warning labels inside this trunking of the reason it's there.

Just means chipping out some plaster behind in a few places so I don't hit the cable haha
 

Reply to Splitting workshops. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
740
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
519
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock