Sorry, explain please
(Tin hat in place)
a) Attempting to explain where common sense seems to imply --with 2x 2.5 entering a socket in RFC ,that 4mm might be more appropriate for spur wiring...
(ignoring physical constraints of the situation)
b)(or is the situation confused with spur/radial references .. -5 Skill points)
 

Ian1981

Forum Mentor
Messages
2,975
Location
North east
I think 4mm is more suited as Iz has to be higher than In.
Your spur will not require overload protection as long as the load can not exceed the Iz of the spur cable so at most you can only have a max load of 26 amps from one double socket which is highly unlikely that that is what will be used.
2.5mm is more than adequate for a single spur
 

mhar

Electrician's Arms
Messages
655
Location
devon
If you look at appendix 15 you will see that you can spur from the origin in 2.5 which will negate the need for a 20A mcb as you suggested in your post 7
 

wirepuller

Forum Mentor
Messages
5,536
Location
south uk
I see plenty of EICRs stating that 'multiple circuits' are connected into 1 breaker and need rectifying. On inspection it's often just a spur taken from ring at MCB and no issue at all!
This is a common misconception, 'multiple circuits' in one MCB is an impossibility by definition. If there is one point of connection to a protective device at the source of supply it is one circuit no matter how many cables are connected.
 