Have a look at Appendix 15 of the BBB (Page 505)
 
The 2.5mm the spur is made with has an advantage ,
it is not evolved in the current flowing thru the rest of the ring .
(that may already be well loaded)
 

Pete999

-
Arms
Esteemed
The 2.5mm the spur is made with has an advantage ,
it is not evolved in the current flowing thru the rest of the ring .
(that may already be well loaded)
Sorry, explain please
 
Sorry, explain please
(Tin hat in place)
a) Attempting to explain where common sense seems to imply --with 2x 2.5 entering a socket in RFC ,that 4mm might be more appropriate for spur wiring...
(ignoring physical constraints of the situation)
b)(or is the situation confused with spur/radial references .. -5 Skill points)
 

Ian1981

-
Mentor
Arms
Esteemed
I think 4mm is more suited as Iz has to be higher than In.
Your spur will not require overload protection as long as the load can not exceed the Iz of the spur cable so at most you can only have a max load of 26 amps from one double socket which is highly unlikely that that is what will be used.
2.5mm is more than adequate for a single spur
 

mhar

-
Arms
If you look at appendix 15 you will see that you can spur from the origin in 2.5 which will negate the need for a 20A mcb as you suggested in your post 7
 
I see plenty of EICRs stating that 'multiple circuits' are connected into 1 breaker and need rectifying. On inspection it's often just a spur taken from ring at MCB and no issue at all!
 

Deleted member 9648

-
Mentor
Arms
I see plenty of EICRs stating that 'multiple circuits' are connected into 1 breaker and need rectifying. On inspection it's often just a spur taken from ring at MCB and no issue at all!
This is a common misconception, 'multiple circuits' in one MCB is an impossibility by definition. If there is one point of connection to a protective device at the source of supply it is one circuit no matter how many cables are connected.
 

Reply to Spur from 32MCB in the Electrical Forum area at ElectriciansForums.net

Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
Top Bottom