Hi all. I have had a query from a client.
We recently spurred a shower boost pump (400W) off of a local lighting circuit due to there being no local power circuit to connect to. We made an assessment of the lighting circuit loading, deemed it sufficiant to carry the additional load of the pump and installed switched fused isolation for the pump with the correct fuse in place. Can anyone give me good reason why this installation would not comply with regulations (My clients argument). A minor works certificate was issued on completion. Cheers !
 
It is in a school so notification would not apply and it is in a cupboard so not a special location but is RCD protected anyway. Thier issue is the fact it has been spurred from a lighting circuit ?? OK in my eyes ?
 
As long as cable is sufficient, I assume 6A overcurrent protection, then you've done nothing wrong! If you can hae a 500W flood on a lighting circuit why not a 400W pump.

May seem wrong to the untrained eye but they don't know what we know!
 
Nowt wrong with what you have done, IMO. Presumably (since you don't mention it) your load assessment was good otherwise they'd be suffering MCB tripping.

Ask them to detail exactly which BS7671 regulations they believe are broken. I'd be interested myself, as I have put a couple of pumps on lights circuit over the last couple of years.

Do report back.
 
I can see no issues with what you've done mate. Write to the client stating that to the best of your knowledge the installation complies with BS7671 and that if they still disagree to reply detailing their complaint in writing stating the regulation/s believed to be breached.
 
be honest i cant see a problem its fused down presumably to 3 amp , i asked a question to elecsa technical regarding the heater/ light fittings which is a 750 watt load and they said they were not a problem so what you have done in my eye is fine
 
It is in a school so notification would not apply and it is in a cupboard so not a special location but is RCD protected anyway. Thier issue is the fact it has been spurred from a lighting circuit ?? OK in my eyes ?

Special location (still part of the wiring regs), not notification ;)

As it's away in a cupboard then classed as a separate room anyway. As you've used appropriate cable then can't see an issue.
 
Soon as people here the words "lighting circuit" or see a 1.5mm cable or 6A mcb they automatically think its for lights only, not the case. You've done nothing wrong, infact it sounds like a spot on job. As above let them show you in the brb where it says that you can't do it? (long as you've labeled the cu for that circuit)
 
Well there's about a kilowatt of spare capacity for the existing lights
You say its not overloading the circuit,so where's the problem

If the labelling of the circuit is up to date,then alls well

You would not hear cries off the client if there was a fan on a lighting circuit,so other than loading ask them whats the diffference
 

Reply to Spurred pump from lighting circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
681
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Another one that some of you may be interested in.......... We had a call to remove 4 off blackstone generators from a pumping station in south...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock