Discuss Spurs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
P
Peter Woodford
I am currently replacing a fuse board under part p and am carrying out the testing to all of the circuits at the moment and one of the rings there are two spurs one goes out to a pond control panel the other to outside lighting about 10 lights in total what tests do i need to carry out on this equipment or on this ring
cheers
if both spurs come off seperate sockets and the loads are correctly fused down you need to mesure r1+r2 and eli at all points and record highest
however spur off spur is not allowed and any fused spurs should have correct size fuses.
also there should be some rcd times (17th ed)
why are you replacing fuse board if you dont know what tests to do were you not assessed under partp to prove competant
was assessed but was not sure if i need to do insulation resistance test at 250 v because of the controls board for the fish pond am replacing the fuse board this weekend
Reply to Spurs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, Thank you in advance... So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to...
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Evening all, Just a quick question, I am an electrical maintenance engineer and have 18th edition, inspection and testing and so on, so I get...
