Got star delta motor new installation, when goung into run just dies, dosrnt trip over losd, as if contactor not holding in on run. Wrong wiring diagram eith pannel, u1 goes u2, v1 to v2, w1 to w2 on motor windings. Running of a generator, 200kva, 50 kw motor, so man enough. Pannel firm say generator maybe lossing voltage when coming in to run mode. Only tested voltage 238v, 408v when running, never tried under load, any ideas
 
Sorry mate your post is very confusing, a diagram and a better description of what you have may help someone give you advice.
 
So whilst the motor should be running in delta, the windings are configured L1= U1,U2 L2=V1,V2 L3= W1,W2?

If so it's pretty obvious why it isn't working.
 
I have very little knowledge of motors (I can see the obvious one as pointed out above though) but generators are familiar territory.

So, what does the generator do while this is happening? Does it slow down, chuck up a cloud if black smoke, show up any warnings?
Is this the only load on the generator or is there a decent load on it before this motor starts?
Have you tried it with the generator unloaded aswell as under a decent load?
 
I was 4th electrician called to a job where 2 expensive pumps had burnt out. they were wired pretty similar to above and were single phasing. no-one noticed wiring !!
 
I have very little knowledge of motors (I can see the obvious one as pointed out above though) but generators are familiar territory.

So, what does the generator do while this is happening? Does it slow down, chuck up a cloud if black smoke, show up any warnings?
Is this the only load on the generator or is there a decent load on it before this motor starts?
Have you tried it with the generator unloaded aswell as under a decent load?



hi not very good at explaining, 6 terminls on starter, 6 on motor. on motor proved windings labelled correctly, by continuity test u1 - u2, v1 to v2, w1 to w2 are all circuits. starter has 6 terminals, no labelling, manufacture says 2 possible combinations, u1, v1, w1, then w2, u2, v2. or a different combination of the 2's. tried both but wont work.
 
only load on gen, no change of engine noise, smoke, suggested could be a volt drop when changing over?, never checked it with meter / or on gen volt meter, going back so will check, thanks
 
Edit: just saw recent post. That looks OK as given, or V2, W2, U2. I think we all thought you meant U2, V2, W2 (which is open-circuit to all lines) and the other three are the wrong sequence and will cause single-phasing.
 
Edit: just saw recent post. That looks OK as given, or V2, W2, U2. I think we all thought you meant U2, V2, W2 (which is open-circuit to all lines) and the other three are the wrong sequence and will cause single-phasing.

thanks, wrong wiring diagram with panel so didn't help ,i'm only used to connecting up, not got any knowledge with fault finding, tracing wiring through starters. hopefully right diagram and if manufacture marked terminals would be easier. is there a sequence ie L1 u1 and say V2, L2 v1 w2, L3 w1 v2, so I could trace wires back, like on a line drawing. or is it just the order of the manufacture.
 
If you suspect either the panel is wired wrong (possible) or the drawing is wrong , then I would identify the MC, DC and SC contactors and just follow the wiring to the terminal blocks at the bottom. There are plenty of star delta wiring diagrams on the internet which will show how to connect the 6 motor wires. As for the motor, hopefully that is labelled correctly otherwise again you will need to test that out. Coincidently I am just about to leave home to connect up a 90KW jobbie, hopefully it wont go bang. lol
 
Looked at diagram I had in van and was same, went back last nite 2 of us, I stoped at gen, taking 415v ,160a, start, when drops into run voltage goes to 385v, engine changes tune bavk to 415v, fans dropping out due to volt drop ??? Cant be anything else. Hope your motor when well, thanks
 
Quick update, thanks for the positive comments, generator firm came out swapped avr? Still wont start the fans, took generstor away ( stamford) came back with a meccalte, adjustable avr? Fires up and runs the fans a treat, thought I was going mad, just very grey now
 

Reply to star delta - generator in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hi Guys, Is my understanding of why it is bad for a star/delta motor to be stuck in star correct? 1) Star delta starting is used as a method of...
Replies
14
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock