A little help required if you would please chaps;

Been a hard week and i cant find or remember what i need to know.

In order to light a commercial store room i need to re-install lots and lots of lights, they are 6 foot twin flourecents, the question is how many can you run off one B6 MCB (allowing for start up current) so i can work back to switch quantity/cable sizes or is there a formula somewhere that i've missed.
or is there a rule of thumb allowance per fitting
thanks in advance
 
Advertisement - Content continues below
G

Guest123

  • Thread Starter Thread Starter
  • #2
Hey mate, would those 6ft fluo's be switch start or high frequency??
 
M

maddfridge

  • Thread Starter Thread Starter
  • #4
A little help required if you would please chaps;

Been a hard week and i cant find or remember what i need to know.

In order to light a commercial store room i need to re-install lots and lots of lights, they are 6 foot twin flourecents, the question is how many can you run off one B6 MCB (allowing for start up current) so i can work back to switch quantity/cable sizes or is there a formula somewhere that i've missed.
or is there a rule of thumb allowance per fitting
thanks in advance

hi there
from the dark side the figure of 1.8 comes to mind to allow for start up current


design current = watts X 1.8 divide by 230

check cable current carrying capacity and voltdrop and the rest of the cable sizing stuff
cheers
 
M

MrTrance

  • Thread Starter Thread Starter
  • #5
^ Absolute correct, 1.8 is the start up current factor for flouries and maybe you could use more 6A MCBS for the job... we did about this last week in college, diversity and spreading them equally for 3 phase boards :)
 

andyb

-
Arms
Esteemed
The 1.8 you mention is not the starting current but for the running current.
It's to take into account the load associated with the control gear and the power factor when not known.
Therefor if you work out that the operating current of the connected fittings was for example 5 amps, without any other infomation re the power factor or control gear you should multiply this by 1.8, so your maximum demand for that circuit would be 9 amps.
 
W

wattsup

  • Thread Starter Thread Starter
  • #7
(flus are prone to hate cold weather) I would allow 100watts for each 6ft twin fitting, I'm over the top I know, but you will not go wrong with that in mind. Assuming no vd and supply feeds are within scope.
In effect 10 x 6ft twins per 6amp breaker, start up will be higher than 6 amps but it will not trip the breaker. Once running about 3.5amps
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to start up current for flories in the Commercial Electrical Advice area at ElectriciansForums.net

CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom