How's this for a means of earthing this steel conduit is acting as a tt arrangement, although brilliant ze readings, 6.41 ohms 34a. What do you all think to this.
Discuss Steel conduit in the UK Electrical Forum area at ElectriciansForums.net
Looks like 1" conduit to me, not sure about the tt bit, does the conduit go underground? If so it'll no doubt be corroded as it's b/e, not a good idea at all!
How have you conducted your tests?
your misses will know the answerYes the conduit goes into the ground, no way will I get a better Ze reading with a earth rod, just wondered if any1 else has come across this
Disconnected main earth and carried out EFLI test on high current
Disconnect bond on that copper pipe and see what you get. lol Bet it won't be so good.
Nah freakin gas pipeCould be 'pin grip conduit'. Very old, haven't seen it for years.
Could well be.Nah freakin gas pipe