Hi All

Question - a Dimplex 3.4KW storage heater would presumably have a max current drain of 14.78A. Given that 2.5mm T&E is rated at 20A on a radial, would it be ok to run it in 2.5 T&E on a 16A MCB? Reason I ask is that I have only ever seen storage heaters run in 6mm (maybe because there were more than one heater on the radial?)
I would be running each heater on it's own radial

Thanks
Andy
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below
A

andyww

  • Thread Starter Thread Starter
  • #3
Thanks Mark

Not had any experience of storage heaters so wasn't sure if they were rated differently and that's why I'd only seen them run in 6mm. - 2.5mm it is then

Cheers
 
S

spark1

  • Thread Starter Thread Starter
  • #7
Just a bit of advice..
If the installation has more than this one heater and they are all in the same c.u [usual setup], then I would install a 20A c.b rather than the 16A. Reason being that when all the heaters are initially switched on the circuit breakers can be loaded close to their rated current..if the c.b is not of a high quality then they tend to heat up. this combination of warm circuit breakers in close proximity to each other can in the long term have a detrimental effect on the c.b .and in some cases it can also trip it under full load: hence the reason in this instance for advising the 20A c.b...more tolerance to the thermal trip .


spark1
 
R

revolt3k

  • Thread Starter Thread Starter
  • #8
I've only ever seen Storage Heating wired in 2.5 T&E. I guess if the rating was large it would need a bigger cable (4 or 6 mm) but norally in domestic there on 2.5's

A Question i have tho is, when testing you can only do the dead tests as the power doent come on till late. How do you carry Ze and PSCC/PFC test out to calc Zs?
 
i put zs down as a limitation and just do dead tests inc r1r2 ,as for ze again verify cpc continuity all the way back to source ie main earth bar and record a lim
 
Last edited:
S

Spudnik

  • Thread Starter Thread Starter
  • #10
Your Ze should be the same as the main CU.

As for Zs, this could be calculated and noted on the cert.
 
S

spark1

  • Thread Starter Thread Starter
  • #11
I always rig up a temp supply from the general supplies consumer unit to the off peak c.u and carry out a full functional powered up test. Reasons being.........

1. Confirmation that all will be well when the teleswitch powers up ,usually when the residents are in bed...peace of
mind scenario !

2. To allow all coatings of heating elements to be burn off at time of installation preventing unwanted fumes possibly
circulating in rooms inhabited by sleeping persons....especially children.



spark1
 
Last edited by a moderator:
S

Scott F

  • Thread Starter Thread Starter
  • #12
Only thing with that is you have to be CERTAIN there is not an afternoon boost.
Otherwise R1+R2 you think your working dead,afternoon boost kicks in BANG
 
Advertisement - Content continues below

Reply to Storage Heaters Dimplex 3.4KW in the Electrical Forum area at ElectriciansForums.net

Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom