HI all
I know neutral faults can be hard to find, different techniques are aways good to learn.
I went to a clients house to fix a faults and look at the ability of the house to accept a new modern board. They almost drilled though a cable stopping before they went thought the whole cable.
I am to return to the clients house, to find the remaining fault.
During testing end to end on line/line is 0.40ohms like wise for neutral/neutral but if I connect the my meter, one clip line and one to neutral (at DB) you get a continuity reading 13.95 ohm this is with all conductors disconnected from the board. this is a house they have just bought. So i am guess this fault has been around for a long time.
I have corrected the sockets that high/fluctuating reading and confirmed that the polarity on all the socket is right.(loss connections) As this is stranded 2.5 mm could it be a possibility that a couple of strand have strayed in one of the sockets that I have not taken off. or that some of the sockets be faulty. they are the newer style design MK so not the sockets that would have been put in the house.
When I go back I was going to start braking up the ring until i loss continuity but this can be time consuming and you have to put it all back again. At and you can make more problems.
Does anyone have any other suggestions/technics.
Bits of back round.
The board old rewardable ceramic holders. there is only two circuits in the whole house one ring main and lights. (three bed semi dictated house) lighting is 1mm does not have an earth/CPC
The new fitted kitchen was replaced a few years a go, but the did a poor job of it. they did not make a new kitchen circuit the fitted fridge can not be unplugged or isolated from the circuit with out trying to get the fridge out of its cabinet. it looks like they have taken cable of sockets instead of using FCU to feed washing/dishwasher machine.
I know neutral faults can be hard to find, different techniques are aways good to learn.
I went to a clients house to fix a faults and look at the ability of the house to accept a new modern board. They almost drilled though a cable stopping before they went thought the whole cable.
I am to return to the clients house, to find the remaining fault.
During testing end to end on line/line is 0.40ohms like wise for neutral/neutral but if I connect the my meter, one clip line and one to neutral (at DB) you get a continuity reading 13.95 ohm this is with all conductors disconnected from the board. this is a house they have just bought. So i am guess this fault has been around for a long time.
I have corrected the sockets that high/fluctuating reading and confirmed that the polarity on all the socket is right.(loss connections) As this is stranded 2.5 mm could it be a possibility that a couple of strand have strayed in one of the sockets that I have not taken off. or that some of the sockets be faulty. they are the newer style design MK so not the sockets that would have been put in the house.
When I go back I was going to start braking up the ring until i loss continuity but this can be time consuming and you have to put it all back again. At and you can make more problems.
Does anyone have any other suggestions/technics.
Bits of back round.
The board old rewardable ceramic holders. there is only two circuits in the whole house one ring main and lights. (three bed semi dictated house) lighting is 1mm does not have an earth/CPC
The new fitted kitchen was replaced a few years a go, but the did a poor job of it. they did not make a new kitchen circuit the fitted fridge can not be unplugged or isolated from the circuit with out trying to get the fridge out of its cabinet. it looks like they have taken cable of sockets instead of using FCU to feed washing/dishwasher machine.