Right, so its been one of those long days.

swift breakdown:
top floor flat.
lighting cable is single cores in a conduit system.

was employed to install downlights in 2 rooms.

Really bizarre one for me, ive never encontered nything like this before.

So i tested the original fittings in these rooms to establish an earth path, all was well.
1.16 zs.

wired all my downlights and then crimped onto the switc and neutral at the original fitting.
zs was 1776.

disconected my wiring, still 1776 ohms.

this was the same for both rooms.

ran a new earth from the MET (10mm)
the done a zs with that new earth and across the switch/neutral at the light.
still getting 1776.

Really confused as the ze on the property is really low (0.25ohms)

this problem is only happening on this lighting circuit.

Any ideas on this?

i had plan to wrap up for the big quarantine but ill need to go back out tomorrow
 
Is the conduit being used as the CPC? Any RCD protection on the circuit? If no RCDs, is it possible the high current Zs has damaged the earth path?

Is it possible there is a crappy joint in the line conductor somewhere? I might check a few other light fittings just to check.
 
the conduit has flying leads from the end boxes but connected with them appears to be dedicated earths through.

its an old board and the circuit is on the no rcd side of the board.
think its 3036 mcbs

i'll definetly look into the possible crappy line conductor.
its got be surely?
new earth ran in off a proven good met and still getting the bad reading.

there have been only a couple of noticable alterations to the original wiring
(lowered bathroom ceiling/ spots)
and a horrible looking cupboard light wired from another dimension where it appears bs7671 is not high on the agenda :)
 
If a new continuous conductor back to the MET is giving such a poor Zs, and assuming the circuit works, then the logical answers are either a failure of the external earth or a problem with the tester or test leads.

Yeah everything seems to work fine.

I don’t think it’s the meter because why would I get good readings on the other circuits and when doin the ze?
 
If you have installed additional lights it will now require additional rcd protection. Sounds like you have disturbed something with your new works.

I thought you only had to install an rcd on a new circuit?
Not an an alteration of an existing circuit that doesn’t run through a bathroom?

yeah I’m goin to review the works I’ve done when I get there :/
Goin to bypass the dimmers I’ve put in as well.
Struggling
 
If you have installed additional points it must comply to current Regulations, your part at least and this means additional rcd protection. All lighting circuits in a dwelling now require additional rcd protection this applies to new circuits and additions to existing.
 
If you have installed additional points it must comply to current Regulations, your part at least and this means additional rcd protection. All lighting circuits in a dwelling now require additional rcd protection this applies to new circuits and additions to existing.

right I’ll just move it onto the rcd side of the board then.
This also might tell me more if it starts tripping out
 
Right!!!!!
I’ve took out the dimmers and put the connections in block.
Now getting 1.37.

could it bdd red faulty dimmers?
Cknndctions were good on these.

No, they're not faulty, they're dimmers, they are designed to restrict the flow of electricity so of course they will restrict the flow of the test current and give a high reading.
 
A dimmer switch isn't a resistor as such and under fault conditions the triac will close allowing fault current to flow.
 

Reply to strange earthing problem (lighting) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
510
BMS installers have attended. After fitting the panel they also replaced the aged lighting in the boiler room with 6ft LED battens as instructed...
Replies
5
Views
884
Hi all, Replaced a ceiling light yesterday (I'm a novice but confident with basic electrical work). All was well and working, so I turned off...
Replies
13
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock