Was at a callout today kettle plugged into cooker control switch was not working and neither was the cooker.Unplugged the kettle and put my megger in and im getting 248v.Disconnected the cooker and getting the same at the outlet.Changed both the switch and outlet and rcbo however still the kettle or cooker does not work.Tried other appliances in the socket too and they dont work either yet still getting 248v .

Any thoughts?
 
Was at a callout today kettle plugged into cooker control switch was not working and neither was the cooker.Unplugged the kettle and put my megger in and im getting 248v.Disconnected the cooker and getting the same at the outlet.Changed both the switch and outlet and rcbo however still the kettle or cooker does not work.Tried other appliances in the socket too and they dont work either yet still getting 248v
what you put in the first post ,we are not mind readers you know .
 
High resistance joint on the L (or N). Simple application of Ohm's Law. If you're not pulling any current (I imagine your megger has a high input impedance) then the voltage drop over even a largish resistance will be low, and you will measure a high voltage. Whereas anything pulling a reasonable amount of current (with a low resistance), the majority of the voltage will drop across your high resistance joint.

Hence Handyspark's question, I guess... :)
 
Thanks happysteve i looked for a joint but couldnt see any.

It might be under the floor or in the wall tho so ill prob end up rewiring it.

Or it might be in the service head, meter, isolator if fitted, a loose henley block connection.

I would put the system under some load and check the voltages all the way through the system. That will help point you in the right direction.
 

Reply to Strange things at callout in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock