Hi, carried out an inspection this week on an installation which consisted of two phase three wire to a small building from an electrical switch room. The supply is wired using 25mm LSF/SWA protected by BS-88 at the sub. At the building the supply is terminated into a 947-3 isolator and then reduced using various tails to smaller DB's and fused isolators. The tails vary between 4mm and 16mm depending on the circuit demand for example the single pole fused isolators are rated at 32A and fed by 4mm tails, the larger 9-Way CU's are fed using 16mm tails. Reading 433.3.1 would you consider this to be satisfactory as the fault protection at the load side of the install is satisfactory for the supply tails? IMHO I am thinking they need to provide local protection at the installation and then size the tails accordingly? This install is approx. 25 years old and no history of overload. I clamped the load whilst carrying out the inspection and the install was only drawing 6A. P.S The two phase supply is another question for later;)
 
Sorry for the confusion, basically 25mm sub mains supply to building. 100A BS-88 protection at source.
In building the 25mm terminates into a non fused isolator where it splits to smaller 4mm/6mm & two 16mm single phase sub feeds to local fused isolators and two 9-way consumer units within the building. The fused isolators are rated at 20A & 40A and the CU's taking diversity into account demand approx 30A each.
My question is, should there be fuse protection where supply cables reduce from 25 or am I right in thinking reg 433.3.1 is applicable?
 
Still not really sure what you're saying? Are you suggesting the 100A BS88 is protecting 4,6,16mm cables or am I just too tired to read?
 
Quite easy to suggest the appropriate improvement.
It must be your call, though, otherwise we also carry the liability and, of course, our commission.

What coding would you suggest?
 
Yes sorry its been a long week! My explanation is a bit complicated but basically the 4/6/16mm tails are protected by the 100A fuses at the source. the supply from source enters the building as a 25mm SWA then reduces.
The load on these cables though is protected by local fuses which are fine for the 4/6/16mm tails.

IMHO I am swaying toward C3 with a recommendation for future local protection to be provided to the tails if the installation undergoes any further alteration. its a small gymnasium and so we will be inspecting it every three years and we carry out other inspection work annually so we can at least keep up with any works.
 
Yes sorry its been a long week! My explanation is a bit complicated but basically the 4/6/16mm tails are protected by the 100A fuses at the source. the supply from source enters the building as a 25mm SWA then reduces.
The load on these cables though is protected by local fuses which are fine for the 4/6/16mm tails.

IMHO I am swaying toward C3 with a recommendation for future local protection to be provided to the tails if the installation undergoes any further alteration. its a small gymnasium and so we will be inspecting it every three years and we carry out other inspection work annually so we can at least keep up with any works.

So everything is protected then?
 
The 4, 6 and 16mm tails are protected for overload even though the protection is upstream so no code IMO. The title of your thread is FAULT PROTECTION but what you have explained points more to overload protection. Can you elaborate a bit more.
 
The 20A fuses are at the load end of the tails. From the fuses are final circuits, for example Shower & a Sunbed. The tails are backed up by 100A fuses, final ccts protected by 20A fuses. Tails wired in 4mm/6mm. Final ccts wired in 4mm T+E.

Wish I had a photo to show the layout.
 
Think about it this way you have a circuit with a fixed load protected by a 20A protective device. This 20A protective device is fed with 4mm tails from a 100A fuse. How can the 4mm tails get overloaded?
 
In all seriousness I'm not on here to get involved in the competent/non competent persons debate, I'm a little old in the tooth for that.

I am after some opinion on an installation I have come across this week that I thought I would share with you(rather badly I admit) and see what other people's thoughts are. Don't need any sarcastic remarks please
 

Reply to Sub distribution supply fault protection question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
696
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock