Hi all,

Trying to get my head around an external install to a garden shed.

I've run a 4mm H07 cable for the distribution circuit radial from the house. The 4mm is appropriate for VD over the distance. The cable is protected by RCD at the main consumer unit and a 20A MCB and travels up the garden clipped to a concrete wall. Then into the shed.

If I install a consumer unit in the shed, do I need to run a seperate earth cable as well? My head is saying no, its no different to running a radial, yet I keep thinking, consumer unit, seperate earth?

The installation is TN-C-S PME

The CU in the shed will be populated as:

100A Main Switch
16A MCB, 2.5mm T&E for socket radial
6A MCB, 1.5mm lighting circuit

Can someone explain why I'm getting confused?

Mikey
 
If there are no extraneous parts in the outbuilding then you are unlikely to need any additional protective conductors.

Why are you fitting a CU in the outbuilding? The 16A MCB is completely pointless when it is fed by a 20A MCB
 
as dave's post. why not feed the 4mm direct into socket/s and add a SFCU (5A) for lights?
 

Reply to Sub main earthing/CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
933
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
527

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock