Hi everyone,

A local pub is changing one of there function rooms in to a cafe, there plan was to have all gas equipment so i done the cable calcs and installed a 16mm 3 core swa as the submain cable from the main 3 phase db in the pub to what was going to be a single phase db in the cafe.

Then the gas man has came out to install the gas pipe and has advised the owners they dont have the relevent gas supply for the amount of gas they would need for all gas appliances, so now the want to use a couple of full electric appliances.

So i am now going to run a 3 phase 16mm swa submain from the main 3 phase db in the pub to a 3 phase db in the cafe.

As they have already spent around £200 on a cable thats now no use, and the cost of adding extra points they are trying to save a bit elsewhere.

So my question is can i use the steel wire armour of a 16mm 4 core swa as my main earth for the new submain, or will i need need a 5 core swa, the run is around 35m, i would always just go for the 5 core but im just trying to see if i can help them at all.

thanks for any advise
 
Yes you probably can.

have you done any calculations for R1 & R2?

If you have a Ze, then do the calculations and post here for a sanity check if you are a bit rusty.
 
The Prysmian data sheet for SWA has 16mm 4C as R1 = 1.15 ohm/km and R2 (armour) as 3.1 ohm/km. From your supply Zs and length you can check if the planned OCPD will disconnect fast enough.

If the armour R2 is too high it might be worth seeing if a separate 10mm CPC is enough (1.83 ohm/km) as that is probably cheaper than going to 5 core SWA.
 
Actually if the 3-core SWA is in and supplying a CPC from the single phase plan then adding 4C for 3-phase in the one cable but using that for sufficiently low R2 should be OK.

Make sure both ends of the armour are properly linked to the earth bar / CPC arrangement by a suitable pig-tale style link to the banjo or Piranha / Earthing nut.
 

Reply to Submain for a cafe in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
343
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
692
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
692
Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
344
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
452

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock