Evening, may I pick you brain guys?
I have wired a summer house about 30m away from the main board. I have used 32A at DB1 (not RCD protect) and 6mm² 3core SWA, where I have connected both black and sheath (sleeved) at both end as CPC. In the Summer house I have used shed consumer unit 1xRCD and 2 useable mcbs.
I test Ze and PFC at DB1. I then move to test the shed DB2 RCD, Ring final and light circuit.
I am wondering
1. if I use Zs at the DB2 as Ze while filling the cert or do I use Ze and PFC from DB1?
2. I have added a 32A mcb at DB1, do I test the whole DB1 or Ze and PFC from there are enough?
What are your thought guys?
Regards
 
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Advertisement - Content continues below
Ze and PFC are done at source, Ze only occurs at source assuming you have not TT'd DB2. There is no need to test all circuits from DB1, just your new circuit.
 

ferg

-
Arms
Esteemed
One section of the EIC is for supply characteristics and the SOTR is ZS and IPF at DB
 

Welchyboy1

-
Arms
Esteemed
Usually on the top of the test results section page of the cert there is a box for zs and ipf reading at origin of your remote 2way cu, but this is only on the last test results page, its always worth measuring these values as part of your testing imo
 
  • Thread Starter Thread Starter
  • #7
Usually on the top of the test results section page of the cert there is a box for zs and ipf reading at origin of your remote 2way cu, but this is only on the last test results page, its always worth measuring these values as part of your testing imo
Thanks guys, just to clarify, am looking at the test sheet part 10, I can see PFC bit and a column of Zs measure near the end of RHS.
I am wondering am missing the Zs box
 
Test Meter - Forum Sponsors since 2007!
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Summer House Submain in the Electrical Forum area at ElectriciansForums.net

Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom