Upright Sunbed.
63A supply in 16mm SWA
63A type C MCB to deal with initial inrush of current.
100mA RCD was recommended by manufacturer As 30mA Would cause nuisance tripping.

Maximum earth fault loop impedance value for 63A type C MCB is 0.27.
Ze is 0.21

How do I meet this value? Is there anything I could change to install to increase the max EFLI?
Thanks
 