The attached photo shows the suppliers head that includes an earth terminal.
The incoming supply cable is a single phase plastic sheathed cable containing L & N.
The earth terminal is not actually connected to anything (not internally linked).
The DNO is SSE.

A previous contractor was under the impression this was the suppliers earth and used it for earthing.
However, they did leave a comment that the earth impedance was "a little high"!

Historically the property was TT, but there is no longer any sign of an earth rod etc.
This is a fairly old property, now with a number of somewhat less-old properties nearby.
Likely the original supply was overhead, before the area got developed a few decades ago.

Question:
With this head fitted, with an accessible earth terminal, would it be correct to say the DNO has supplied an earth?
And in which case they should maintain it?
Or are there circumstances when this head would fitted but with the earth terminal not connected?

Ideally one would simply ask SSE what type of supply is available, but this seems to be proving difficult.
If it is reasonable to say this should be a supplier's earth, I'm tempted to log a call to say the earth appears to have failed.
 

Attachments

  • SSE Intake.jpg
    325.9 KB · Views: 94
I'm sure I've seen that type of head on a TNS setup, obviously without a link inside, exactly as you have but with a TNS earth coming from the suppliers cable. So I don't think the head style can be used as proof and there is apparently no evidence (like a PME sticker) that they ever supplied one.
But equally you also aren't really supposed to know there is no link inside so maybe playing a little dumb might get a visit sooner rather than later and if PME is available it might simply get sorted there and then.

Is there still an up front RCD? If for whatever reason SSE don't treat it as urgent this is a bit tricky isn't it.
 
Haha that's a good one. Will be interesting to hear their response. 'No, not an earth terminal, wherever did you get that idea? It's a decorative accessory.' Perhaps you should put an earth symbol sticker on before sending them a pic.
 
Is there still an up front RCD? If for whatever reason SSE don't treat it as urgent this is a bit tricky isn't it.
There is no up-front RCD, but a reasonably modern consumer unit with RCD protection for all circuits (2-pole RCDs, in a dual RCD plastic housing).
Have you looped direct to it with that earth disconnected.
I have carried out a number of loop tests, there is some earthing from bonding to gas & water pipework, with a value of around 55 Ohm when all connected. There is no earthing at all from the terminal (meter won't actually execute a loop test), and it is open circuit to N.
 
To my thinking it would not be unreasonable to report a failed earth as there is no present evidence of TT, or TNS, and at first glance it looks like TNCS. If they agree to investigate without delay fine, otherwise I'd feel I couldn't really walk away without bashing a rod in.
Of course the fact the property has a working neutral destroys the argument, but they might not ask that on the phone!
 
The presence of an earthing terminal on the side of a DNO service head is NOT proof that an earth terminal is provided. This is a mistake I made many years ago, and was told this in no uncertain terms by the engineer that attended when we complained.
 
Isn't it around £150 to provide PME at an existing suitable cut-out as long as the supply is suitable?
Might be best to provide a temporary electrode so earthing isn't via services and recommend the customer gets this done asap (which will probably mean a 3+ week wait)?
 
The attached photo shows the suppliers head that includes an earth terminal.
The incoming supply cable is a single phase plastic sheathed cable containing L & N.
The earth terminal is not actually connected to anything (not internally linked).
The DNO is SSE.

A previous contractor was under the impression this was the suppliers earth and used it for earthing.
However, they did leave a comment that the earth impedance was "a little high"!

Historically the property was TT, but there is no longer any sign of an earth rod etc.
This is a fairly old property, now with a number of somewhat less-old properties nearby.
Likely the original supply was overhead, before the area got developed a few decades ago.

Question:
With this head fitted, with an accessible earth terminal, would it be correct to say the DNO has supplied an earth?
And in which case they should maintain it?
Or are there circumstances when this head would fitted but with the earth terminal not connected?

Ideally one would simply ask SSE what type of supply is available, but this seems to be proving difficult.
If it is reasonable to say this should be a supplier's earth, I'm tempted to log a call to say the earth appears to have failed.
Wether the incoming supply is PME or not that earth terminal should still be earthed via the DNO. If its a split service then you should be getting an eli reading to it, even if the earth is broken outside you would still get >1. If there's no reading at all I would say that it's a PME system and the PME link was either not installed or has been removed, the only sure way to find out is for the DNO to attend site and check what the feed in is. If its a CNE cable then it's as simple as a link being installed and that terminal is now a usable earthing point.
 
I have carried out a number of loop tests, there is some earthing from bonding to gas & water pipework, with a value of around 55 Ohm when all connected. There is no earthing at all from the terminal (meter won't actually execute a loop test), and it is open circuit to N.
Had a job a while back where it was a TNS supply did a neutral - earth loop test and got no reading called the DNO guy attended site and then called for reinforcements as a large part of the street had no earth after some digging and repairs I believe they finally finished at around midnight after about 10 hours onsite
 
Isn't it around £150 to provide PME at an existing suitable cut-out as long as the supply is suitable?
Might be best to provide a temporary electrode so earthing isn't via services and recommend the customer gets this done asap (which will probably mean a 3+ week wait)?
UKPN seem to do it for free every time I've needed one (assuming that supply is suitable, but pretty much all of them are around here now it seems)

I've run into a similar setup (block was on the side, not top) and made the same assumption before - seen the earth block on the side and assumed, then discovered no internal connection. In that one, they'd upgraded the head to TN-C-S while moving it anyway, so didn't matter.

My guess is that it was part of the design to allow the TN-S earth something to connect into when first installed on a new build? In this case it was a 70s Council House....
 
UKPN seem to do it for free every time I've needed one (assuming that supply is suitable, but pretty much all of them are around here now it seems)

I've run into a similar setup (block was on the side, not top) and made the same assumption before - seen the earth block on the side and assumed, then discovered no internal connection. In that one, they'd upgraded the head to TN-C-S while moving it anyway, so didn't matter.

My guess is that it was part of the design to allow the TN-S earth something to connect into when first installed on a new build? In this case it was a 70s Council House....
I've never known a DNO charge for such work either as it should be done during the installation process or when the cut out has been changed. In all fairness the DNO should fit a seperate earth block away from the cut out with 16mm earth for any further connections to be made
 
I've never known a DNO charge for such work either as it should be done during the installation process or when the cut out has been changed. In all fairness the DNO should fit a seperate earth block away from the cut out with 16mm earth for any further connections to be made
UKPN seem to now fit the earth into a single through terminal block of their own supply, rather than connecting into an earth bar, even if I've provided one. Maybe to make it obvious when they've done it, or some internal rule of their own....
 
Thanks for all the replies.

Opinion seems to vary, and I'm veering towards the customer just asking for the earth to be checked, perhaps giving enough reason to get this done urgently (rather than in 6 weeks), and see if it can just be internally linked there and then (I suspect it can).

If SSE won't provide the earth, then I'm going to have to fit an earth rod, and the front outside (everywhere near the intake) is all block paving, so rather hoping I don't have to!
 
Thanks for all the replies.

Opinion seems to vary, and I'm veering towards the customer just asking for the earth to be checked, perhaps giving enough reason to get this done urgently (rather than in 6 weeks), and see if it can just be internally linked there and then (I suspect it can).

If SSE won't provide the earth, then I'm going to have to fit an earth rod, and the front outside (everywhere near the intake) is all block paving, so rather hoping I don't have to!
If the customer rings SSE and tells them a electrician has reported there is no earth coming into the property they will attend ASAP usually within and hour or two
 
Regulation 24 (1) ESQCR requires the DNO to maintain their earth, they have no choice in the matter. Having said that I have found that the DNO for my area always respond promptly on these matters so no real need to go in with the big guns. Clearly no earth or a high resistance earth is a danger sufficient to phone the DNO on the spot and get them to sort out the earth. It looks like it is a simple matter to rectify so no need for hesitation on the matter.
 
The supplier / DNO earth appears to becoming a big issue in recent times, from my experience of contacting my local DNO's over the last 5- 10 years a lot problem seems to be down to the DNO guy who attends site, earthing problems I have found mostly seem to be where metal service heads have been replaced with plastic and no earth lead has been connected to the PILC sheath, had one and the DNO guy was adamant it was a TT supply as they "all were TT supplies in the area" I pointed out to him that unlike some of the properties in the area this property had never had a mural supply and when the metal service head was replaced the earth from the incoming cable sheath was lost and the PILC sheath clearly had a TNS earth available as the ELI test confirmed this he still wouldn't have it and left telling me to put a rod in so I rang the DNO again and raised a complaint this was followed by a call from an engineer in Glasgow who agreed with me that they needed to fix the earth

So I'm beginning to wonder given the changes to training in recent years are the DNO's praying on the lack of knowledge and experience of some of the electricians out there who don't know how to argue the case although an incoming PVC cable makes it harder to identify what earthing type should be available I usually find a quick knock on a few doors next to a property can also glean some information to press the case
 
The supplier / DNO earth appears to becoming a big issue in recent times, from my experience of contacting my local DNO's over the last 5- 10 years a lot problem seems to be down to the DNO guy who attends site, earthing problems I have found mostly seem to be where metal service heads have been replaced with plastic and no earth lead has been connected to the PILC sheath, had one and the DNO guy was adamant it was a TT supply as they "all were TT supplies in the area" I pointed out to him that unlike some of the properties in the area this property had never had a mural supply and when the metal service head was replaced the earth from the incoming cable sheath was lost and the PILC sheath clearly had a TNS earth available as the ELI test confirmed this he still wouldn't have it and left telling me to put a rod in so I rang the DNO again and raised a complaint this was followed by a call from an engineer in Glasgow who agreed with me that they needed to fix the earth

So I'm beginning to wonder given the changes to training in recent years are the DNO's praying on the lack of knowledge and experience of some of the electricians out there who don't know how to argue the case although an incoming PVC cable makes it harder to identify what earthing type should be available I usually find a quick knock on a few doors next to a property can also glean some information to press the case
If the cable is pilc the earth will always be the lead 100% of the time, all new pilc terminations should have a shrink kit applied and an earth braid fitted into the inside of the cut out meaning the top terminal is earthed, however depending on the set up that is already installed depends on what earth is left. If its a pilc supply and the current earth is an electricians clamp directly to the lead this should be removed as it can put stress on the lead and cause corrosion, in this case a shrink kit will be applied and a new earth braid as I said above. However if the earth that is applied to the lead is a plumbed earth it is the norm to leave this in place as it is the best connection type. In this scenario the plumbed earth would generally be ran to an external block at the side of the cut out making the top earth block redundant. Like you say the difficulty lies in proving it on a pvc service as the connection is internal which only the DNO has access to. But in the case of pvc the upper earth terminal should always be earthed via the internal PME link or via the actual earth's from a split service
 
If the cable is pilc the earth will always be the lead 100% of the time, all new pilc terminations should have a shrink kit applied and an earth braid fitted into the inside of the cut out meaning the top terminal is earthed, however depending on the set up that is already installed depends on what earth is left. If its a pilc supply and the current earth is an electricians clamp directly to the lead this should be removed as it can put stress on the lead and cause corrosion, in this case a shrink kit will be applied and a new earth braid as I said above. However if the earth that is applied to the lead is a plumbed earth it is the norm to leave this in place as it is the best connection type. In this scenario the plumbed earth would generally be ran to an external block at the side of the cut out making the top earth block redundant. Like you say the difficulty lies in proving it on a pvc service as the connection is internal which only the DNO has access to. But in the case of pvc the upper earth terminal should always be earthed via the internal PME link or via the actual earth's from a split service
From the two DNO's in the areas I work the shrink kit and braid earth is ENWL's solution which is quite neat and tidy while SP Energy Networks use something similar to a "jubilee" clamp around the PILC for the earth with a 6491x 16mm earth cable connected to it and a sheet rubber self adhesive wrap around it which looks quite bulky and a bit rough
 

Reply to Supplier earth terminal on intake in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock