Discuss supply cable sizing in the UK Electrical Forum area at ElectriciansForums.net

ronky

-
Reaction score
0
Hi ,I have a wood cabin outside 70mtrs from house incoming supply, I was thinking of using a 35mm 2core pvc/swa, as I think a TT system would be appropriate for the cabin, owing to the distance away from house load would be allowing for diversity would be 51amps, seems a lot but it will be a live in dwelling with all requirements for cooking heating etc,am i correct with supply size Thanks ron
 
What's your installation method, earthing arrangement, bonding requirements?
 
PVC/SWA would be buried in the earth at appropriate at depth
my calcs as follows , volt drop table 4E4B 1.85mv/a/mt 35mm =1.35 x50ampsx70mtrs =4.72 volts . 25mm = 1.85mv/a/mt x50amp x70mtr= 6.47volts so not much lighting load so 5% of 230volt=11.5volts allowed and 3% of 230volt =6.9 volts so would the calc with 5% be okay which is 11.5 volts am I getting to tied up ronky
 
Your volt drop needs to take into account the circuits within the cabin not just the distribution circuit.
 
Whilst cable size has been worked out to 25 or 35 due thought needs to be given to the terminal sizes and termination practicalities.

You can buy pin lugs to reduce 35mm to 25mm, since the 35mm size is only required for VD an not load, there is no issue in this solution.

Don't see why at that size you can't use the house's earthing system. Utilizing the armor of the SWA as a CPC. Unless you have extraneous services entering the outbuilding.

A switch fuse would be more ideal to provide protection for this cable, purely to meet discrimination with MCB's that I presume are going to be installed in the outbuilding.
 
Last edited by a moderator:

Reply to supply cable sizing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
623
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
343
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
935
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
453

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock