Can anyone tell me if its a requirement to install a surge protection device to a sub Distribution Board if it serves external equipment ie a roof mounted extract fan even though a SPD is located on the Main Panel?


Sent from my iPhone using Tapatalk
 
Your risk assessment will tell you whether surge protection is required and at what level.
A SPD at a main incomer will be rated differently than one at a final distribution point.
If you need accurate surge protection at an accessory then the overvoltage protection would operate at a significantly lower voltage than for a main incomer.

If you are protecting against lightning side strikes then this is not required in the UK as the risk is deemed to be low, however if equipment or services need resilience then it may be that SPD are needed.
 
The UK has <25 thunderstorm days per year and with the calculations in section 443 this equates to no requirement for SPD.
however if there is for example a key public service, bank server, medical system that requires continuous operation and must be protected from being be destroyed by a strike then it may be required to have spd protection.
 

Reply to Surge Protection Device in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Our farm has a main 200 amp panel in the barn which services the barn, an addition to the barn with an apartment, an herb-gardening facility, and...
Replies
12
Views
1K
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
466
Hello! I'm struggling to find an answer to this question online. I'm new here btw - I'm a DIYer with a physics degree Currently when my fridge...
Replies
19
Views
1K
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
504

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock