Discuss Swa buried in the Industrial Electricians' Talk area at ElectriciansForums.net
Swa is OK for outside zone with no RCD as long as other Regs don't require the protection for other reasons ...i.e. special locations etc
Not within special location, drilled through outside wall then chased in approx 500mm down wall to floorboards at a depth greater than 50mm. I wouldnt see a problem exept it was 50mm 4core 160A feeding hotel control panel..
As long as it length and ccc complied to installation methods then ok, if it was run in an area prone to possible drilling for whatever reason then it would be wise to have a layout plan of the cable run available for any contractors likely to work in the area.
Just to confirm, the buried cable is greater than 50mm from the surface of the wall? Daz
Reply to Swa buried in the Industrial Electricians' Talk area at ElectriciansForums.net
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Hi everyone, I intend to bury a 240 volt cable from my house to my barn about 7 metres as way. It will be buried under my tarmaced drive which I...
SWA
Is it possible to put a 16mm swa on a 40a mcb protected by an rcd
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
