There was one of thing I was unsure of. Can SWA be run this close to the gas pipe inlet to the house?
 

Attachments

  • 20191107_161544.jpg
    206.8 KB · Views: 100
  • 20191107_161557.jpg
    130.9 KB · Views: 93
This is in BS6891 somewhere to which I have no copy. There is a required separation but I cannot quote it although 25mm may be cited. Whatever it is there is no gap of separation in your picture.
 
1573148590478.png

1573148627505.png

This is from the OSG pages 23 & 24.
 
At least it's 3 core cable....even if the black earth isn't sleeved g/y.
Disgraceful work throughout, though.
The 'loose' C type gland is for water ingress prevention....how solid is the actual 'earthed' gland connection?
 
Last edited:
Absolutely awful workmanship and live accessible parts to boot! If thats the level of their work do you really want them back?
I'm afraid to say that will be the first course of recommended action from NAPIT. I concur though I am not sure I would entertain them again but any alternative is money.
 
What is that grey flex hanging through the hole by the supply cable feeding? It looks a bit small to be fed from a 20A MCB.
 
Hi - sorry to say, but I too think the swa cable is best replaced as it has been exposed to weather. Try to find a route that avoids the gas supply crossing. If not, perhaps the swa could be passed through plastic conduit that was secured to the wall behind the gas line.

That N in the CU is a good find, well done :) .
 
What is that grey flex hanging through the hole by the supply cable feeding? It looks a bit small to be fed from a 20A MCB.

I'd have to check but I think it's the feed for the sockets in the garage
[automerge]1573380309[/automerge]
Hi - sorry to say, but I too think the swa cable is best replaced as it has been exposed to weather. Try to find a route that avoids the gas supply crossing. If not, perhaps the swa could be passed through plastic conduit that was secured to the wall behind the gas line.

That N in the CU is a good find, well done :) .

Thanks for this, I've requested the SWA to be fully replaced amongst other things
 
As others have said very poor install also I am concerned about the 1.5mm neutral connection next to the Grey cable in the first photo it look like it terminated onto the insulation hopefully there's not much load on that circuit as if may over heat.
 
As others have said very poor install also I am concerned about the 1.5mm neutral connection next to the Grey cable in the first photo it look like it terminated onto the insulation hopefully there's not much load on that circuit as if may over heat.

The outer sheath was completely screwed through. When I released the screw there was a small blue flash ?. I've sorted it though..

Found a second neutral and a earth sleeve of a similar fashion
 

Attachments

  • Screenshot_20191110-211647_WhatsApp.jpg
    57.4 KB · Views: 19
When I released the screw there was a small blue flash
That means the circuit was still live, please don't go messing around in your board without fully isolating it, i.e. turning the whole lot off and testing for dead using a voltage indicator.
 

Reply to SWA sheath, earthing and empty consumer unit space in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Morning, I was just looking for some advice on what other sparks would do for the following scenario:- A detached Garage is going to house a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock