I see you have a 2365 level 2, do you know any electricians who can give you an onsite evaluation.
Afraid not, I did it a few years ago which is why I know the basics
Discuss SWA sheath, earthing and empty consumer unit space in the UK Electrical Forum area at ElectriciansForums.net
I see you have a 2365 level 2, do you know any electricians who can give you an onsite evaluation.
I'm afraid to say that will be the first course of recommended action from NAPIT. I concur though I am not sure I would entertain them again but any alternative is money.Absolutely awful workmanship and live accessible parts to boot! If thats the level of their work do you really want them back?
What is that grey flex hanging through the hole by the supply cable feeding? It looks a bit small to be fed from a 20A MCB.
Hi - sorry to say, but I too think the swa cable is best replaced as it has been exposed to weather. Try to find a route that avoids the gas supply crossing. If not, perhaps the swa could be passed through plastic conduit that was secured to the wall behind the gas line.
That N in the CU is a good find, well done .
Looks like 2.5 T&E to me.What is that grey flex hanging through the hole by the supply cable feeding? It looks a bit small to be fed from a 20A MCB.
What is that grey flex hanging through the hole by the supply cable feeding? It looks a bit small to be fed from a 20A MCB.
As others have said very poor install also I am concerned about the 1.5mm neutral connection next to the Grey cable in the first photo it look like it terminated onto the insulation hopefully there's not much load on that circuit as if may over heat.
That means the circuit was still live, please don't go messing around in your board without fully isolating it, i.e. turning the whole lot off and testing for dead using a voltage indicator.When I released the screw there was a small blue flash
That means the circuit was still live, please don't go messing around in your board without fully isolating it, i.e. turning the whole lot off and testing for dead using a voltage indicator.