• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss Switch gear / Panel board Rating in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Reaction score
0
The Incoming breaker model is Terasaki - S250-PE, 250 Ampere Frame rated for which Ics is 70kA, Category A breaker

The outgoing breakers model is Terasaki - H125 NJ, 125 Ampere Frame rated for which Ics is 85kA,Category A breakers

The bus bar rating is 65kA for 1s.

How should this panel board be specified, 65kA for 1s??. Since both the Incoming & outgoing breakers are of category A breakers, Is it correct to mention the time rating along with the short circuit?

Generally, How is the panel board short circuit is mentioned in the name plate of the board for which the Incoming & Outgoing breakers have different breaking capacity?
 
What does the rating plate state and do you have the test certificate. They are normally rated to the busbar section withstand.
 