Ooh, I'd hedge your bets and post your question on a USA forum as well if you need info urgently. 99.9% of the guys on this forum are working to the UK 7671 electrical regs, there are one or two around with some working knowledge of the NEC but I'm not sure if they'll be posting over the holiday season.
 
...it'll be electrical trainee,everythings faster,bigger and dearer. That said,festive felicitations to our brother in the ion transference facilitation realm...that's ham-shank for "sparky" :icon12:
 
when one entrance is required, if switchboard is 1200A and over 6 feet

is that under condition 3 on Table 110.25 (A)(1) of the NEC

am confused

Do you mean 110-26, 110-25 is lockable disconnectors.

110-26 (A)(1)
Condition three requires a clearance between panels of 3’ for 1-150V and 4’ for 151-600V.
 
You seem to have sections of 110-26 mixed up.

You have to decide if 110-26(C)(2)(a) or (b) applies. Without knowing the layout of the switchroom there’s none that can help you.

You should also follow the recommendations in 110-26(C)(3) with regard to egress.
 

Reply to Switchboard Clearance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
532
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
333
Hi all, currently doing a job at a house where there are 3 switches In the hallway to control the hall lights. All 1 gang switches, one at...
Replies
2
Views
529
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
824
Now I understand why so many people in US have stories of computers blowing up during thunder storms. This is a pretty dumb rule for ground...
Replies
2
Views
482

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock