Discuss Table 4.1.2a/b in Electricians Guide in the UK Electrical Forum area at ElectriciansForums.net
Could somebody please clarify the difference between tables 4.1.2a & b. It appears to me that the difference is in types of circuit breakers - B or C depending upon max test loop impedance. Is this correct and which measurement do they mean by test loop impedance?
basically, a type C requires double the Amps of a type B to trip within the specified times, so the max. Zs is halved.
A circuit breaker will disconnect within 0.1 sec whenever the fault current is equal or greater than the upper limit of their instantaneous tripping band.
For Type B devices this is 5 × In.
For Type C devices this is 10 × In.
The magnitude of the fault current is dictated by the impedance of the fault path which can be measured by an earth fault loop impedance tester. The lower the impedance the higher the fault current and as Type C devices require higher current for any given time the maximum required Zs is lower.
Why are you asking the question? College work?
Reply to Table 4.1.2a/b in Electricians Guide in the UK Electrical Forum area at ElectriciansForums.net
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
OLDBOY
O
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Hi, I am currently studying to become an electrician and keep seeing this question (normally different values) and I am not sure how to work this...