Discuss Taisl & Earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I
irishsailor
Current Regs state that that tails should be 25mm, however WPD recently fitted a Isolator and fitted 16mm tails. Is it acceptable practice for the tails to be uped to 25mm from the consumer end of isolater to the CU??
Also the supply is TNCS and the current Earthing conductor is 10mm, is it acceptable to put Henley block in and up the EC to 16mm
This in a domestic premise
Cheers
Chris
Cheers
Chris
hi chris,
what size fuse is in the cutout. if its 60 amp then 16mm tails are fine. 100 amp and you need new 25mm tails from isolator. earthing conductor needs replacing from cutout in 16mm to new cu either way ;)
Re: Tail & Earth
Flukey
Thanks for your reply, It is 100A cutout so I agreed with what you said. So I will need to ask WPD to fit 16mm Earth. As I said they fitted the tails and fitted 16mm to the isolator. When questioned they stated that was all they fitted. So I will fit 25mm from consumer end to cover my back IAW wjth the Regs.
Re: Tail & Earth
Flukey
its down to you to fit the 16mm earth irish. as with the tails you are only concerned with consumers side of the isolator ;)
Mark
Thats what I wanted to know, is that acceptable practice for me to terminate the earth in Henley Block, and increase to 16mm form there, and get them to upgrade the earth
irish you can not touch the earth where it is connected into the service head you could terminate it in an earth block and put a bit of 16mm in to the cu and get wpd to replace thier bit
hi mark, if upgrading main earth i always connect straight into service head :eek:
is this a big no no then as i cant see the problem :confused:
Some cutouts do not have the facility to remove the main earth from it without removing the main fuse first.
Newer ones do have screws that can be accessed without removing anything.
Guys
Thanks for all the very helpful advice, I think I will cut the earth and put some block in and increase the size from there and contact the distributor to come and increase it from the service head, as looking at the current head it looks like it has only one access, so to be on the safe side.
Irish
will the distributor charge for this service :confused:
Guys
Irish
i would do the same irish if your service head hasnt got the little removable cover
Reply to Taisl & Earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...