hi all
ive been asked to fit a couple of extra smokes a break glass and sounder to a premier sx 4 zone pannel.
one zone was spare so wired the smokes ect fitted end of line all good.
on checking the pannel i found only 2 sounder circuits both in use...end of both ciruits miles away!
so i thought id use the fire relay to fire the extra sounder powering via the batterys.
the manual says 1 amp max for this relay so no probs.
connected up....earth fault led lights general fault led lights alrm sounds ect.
remove the extra sounder wiring and try again...same thing..
then i thought....* i havent fitted 10k end of circuit resistor.....**.
no i can,t think why this is now giving me an earth fault led....(all 4 zone leds also lit) i can reset but the fault returns in around 3-4 seconds.
have i just lunched the pannel.......not the end of the world it part of a few grand job and a new one is cheap enough...or is there more to it.
any help gratefully recived
cheers
vitoboy
 
Hi. You say ends of sounder circuits are miles away but can't you break into the circuit somewhere or make your sounder the first on one of the sounder circuits ? Run a four core fp cable from panel to your sounder. Sounder circuits can cover more than one zone. Don't forget end of line diode is polarity sensitive. Hope this helps in some way.
 
my new sounder is also miles from the pannel on the end of an fp put in by others a few years ago.
im thinking i may have to by another pannel anyhow so ....get one with 3 or more sounder circuits.
 
You cannot wired a siren via the relay, as the cable will not be monitored. Because you have fitted the 10k resistor across the battery or aux supply you have proberly blown aux or battery fuse, and lock the panel up.
 
You cannot wired a siren via the relay, as the cable will not be monitored. Because you have fitted the 10k resistor across the battery or aux supply you have proberly blown aux or battery fuse, and lock the panel up.

cheers tazz
no i didnt fit the end of line to the sounder anyway.
the battery fuse and aux fuse are good.
i think i must have fried the relay ...i wonder if the relay common is grounded to earth.
i must admit that i hadnt thought of the cable not being monitored...
i think my best way forward is to change the pannel for one with 4 zones and 4 sounder ciruits...cb200 im thinking
really i just wanted to know how i damaged the pannel just to understand..
after all the relay should be ok to switch 1A one sounder is not 1A so desipte the fact the cable would not be monitored why has the pannel become damaged?
most systems ive fitted and worked on have been rafiki twinflex............easy as pie.
i have a feeling that what i am trying to do cant be done correctly with the pannel i had anyway..?

cheers vitoboy
 
Dont want to sound nasty, but Rafiki and Tate panels are the real low end, sold by electrical outlets, and very troublesum kits. Kentec, Firesense and Ctec and good trouble free systems, with kentec and Firesense offering Twin wire option. This would turn what you have into a twin wire by just adding base sounders were you need more, and keeping the detectors and call points without rewiring.
Hope this helps
 
Dont want to sound nasty, but Rafiki and Tate panels are the real low end, sold by electrical outlets, and very troublesum kits. Kentec, Firesense and Ctec and good trouble free systems, with kentec and Firesense offering Twin wire option. This would turn what you have into a twin wire by just adding base sounders were you need more, and keeping the detectors and call points without rewiring.
Hope this helps
cant really comment on that tazz...im really a sparks not a full time fire alarm engineer so have only fitted about 20 complete systems from scratch in my life.
that said ive never had a problem with a rafiki system...aways been very stragiht forward.
but im not the end user or the man who needs to service the system after a few years.
as for the tate pannel im sure its lowest of low end...but its what was on the wall when i got there.
the main problem with any of this is just cost...i can tell the client all day how he should have a decent pannel but i know he will always take the cheapest option...its in afree house pub in cornwall and im sure he has enough problems just keeping his doors open.
ill have a look at the pannels youve suggested for future refence though.
ta
vitoboy
 

Reply to tate premier sx 4zone pannel problems! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
Hi, My alarm system is a Texecom control unit (Premier 64-w) + Keypad + Sounder, and is using the wired zones 1-4 only, with no additional...
Replies
2
Views
2K
Hi everyone, We are working in a large property with a 4 zone fire alarm system installed. The fire panel gave up and the customer has...
Replies
2
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hiya. For anyone interested in domestic fault finding I had a funny one today... Customer complained about her bs 3871 popout kept popping on...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock